I really appreciate the advice. I will increase the heater circuit to 20A, ensure everything is grounded properly and will use GFCI/AFCI combo-breakers on the board accept for the outside sockets as they are already GFCI protected. In this case, I will use just AFCI breakers on the...
Good Afternoon. The cabin currently has no electrical installation. I will ensure two ground rods are installed. Have I chosen my board breakers correctly?
Good Day;
I am installing an external portable 4KW, 30A generator to my small mountain cabin. I have accounted for an external generator hook point, external 30A fused disconnect leading to the internal 12-way Square-D power distribution board. An external 4ft copper ground rod provides the...