ABB / Power One UNO's and TRIO's - 3.0, 3.6, 10.0, 12.5, 20.0, 27.6 use passive cooling - therefore no fans. The IGBT s are strapped against the heat sink and use air convection for cooling. The newer TRIO's - 20.0 and 27.6 have a small fan inside to cool a capacitor set on the A/C filter...
If the RCD is tripping ( this protection device has a test button on it) then it could just be a case of changing it for a RCD that has a higher mA tolerance. 30MA can nuisance trip a lot on solar PV inverters. If an MCB is tripping it would be a good bet it is an internal fault in the inverter...
Thanks. Yeah that seems logical to me, but I can only see use for it in special circumstances. As I see it the lower the test voltage you can use to confidently prove a cable the better. As we all know the higher the voltage used the more dangerous it can be if something should go wrong...
No need to be so hostile dude, chill.
Yes the cable is rated up to 1000v, but that just tells you limit of the insulations properties, right?
My thinking is that if the circuit operates at 325v max, then 500v is closer to that voltage than 1000v, therefore would give a more realistic reading...
I agree, but why do a 1000V ins res test?? In my opinion a 500V ins res would give more realistic results. I don't even know in what situations you would use the 1000V ins res test.
To the OP, I've have never seen a conductor change colour like this. So can't give any suggestions. Heat would be...
Good point and since it's an older install I won't argue that their will be an increased likelihood of nuisance tripping.
Actually think there is regs against one 30ma rcd protecting the whole install. My bad.
I don't like these old 3036 consumer units, make's everything more difficult. =)
I...
Why not replace the 100ma RCD with a 30ma RCD and give the whole distribution board 30ma protection? Then you've killed 12 birds with 1 stone =). Correct me if I'm missing the point here.
Zs=0.04Ω
V= 230V
230/0.04= 5750A
-----------------
I=5750A
T= 0.025s (Read this from you post, also agrees with regs)
K=115
S = √((5750²)x0.025)
-----------------
115
S= 7.906 mm²
So with a 10mm² you will be oversized by 21%...
Did you take an educated guess of the cable size required or did you figure it out? You could easily prove his error in thinking you need 6mm2 by showing him the current carrying capacity's in the regs.
I agree with these guys, you should have stood your ground and defended your decision. If...