    LIVE EARTH WHEN REWIRING DOUBLE DIMMER

    Thank you for that information. I have never encountered such a problem in my 79 years, although I have lit a flourescent tube by holding it under the low pylon cable so can understand what you are saying.
  2. E

    LIVE EARTH WHEN REWIRING DOUBLE DIMMER

    Unfortunately the conversation with her electrician is reported secondhand, he said that the wrong lamps in another dimmer were causing the problem.
  3. E

    LIVE EARTH WHEN REWIRING DOUBLE DIMMER

    I wasn’t at my own home so just tested the earth wire with electric screwdriver which showed same bright orange as the brown wires
  4. E

    LIVE EARTH WHEN REWIRING DOUBLE DIMMER

    I have carried out home wiring for 60 years as a competent person, for the last 20 years, I employ a local electrician to check my work and sign it off. My new partner’s dimmer switch failed, the push button would not push, so I purchased a new unit. I turned off the MCB for First Floor Lights...
  5. E

    9.5kw Galaxy unvented heater trips RCD

    I have sent him an email as I did not get a reply to answerphone. I would not have known if a problem existed until I put in the only heavy load in building. I had Electrician check out the work last year anyway!
  6. E

    9.5kw Galaxy unvented heater trips RCD

    Thanks James. No Idid not bypass the CU OTHER than to prove that fault is unlikely to be with the appliance??
  7. E

    9.5kw Galaxy unvented heater trips RCD

    Please if you were here, what would you do first. This CU is 7 metres from a 1570190274 I left n message on his answerphone yesterday, but not having a reply tried this forum!
  8. E

    9.5kw Galaxy unvented heater trips RCD

    So I have returned to the unit black lead on end of element Neutral) red on Earth 3 Mohms. I then put Black on Earth red on Neutral 0.00 ohms Massively confused, so I checking CU same result N toE = 3M ohms E to N - O.00 ohms 1570189570 Disconnect Neutral to Galaxy. O/L reading on N to E or E...
  9. E

    9.5kw Galaxy unvented heater trips RCD

    Yes Zerax. Problem only occurs when tap is turned on. 1570184669 I have placed the black cap on E and red cap on element. Testing with Multimeter between these two points reads 3M ohms
  10. E

    9.5kw Galaxy unvented heater trips RCD

    This is brand new Galaxy from Screwfix. This problem occurred. Could not find any faults so returned. It is only with replacement thatI query there cannotbe two faulty units, however, tests with multimeter all OK, so E TO L reads 0mV, so replace 10mm cable with 25mm meter tails and replace 40mcb...
  11. E

    9.5kw Galaxy unvented heater trips RCD

    When water is turned ON the RCD TRIPS. 10 metres from CU, 40A mcb. 10mm Doncaster Cable. Changed to 50mcb and 25mm meter tails. still RCD trips?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock