That’s it all complete PASSED.
Basically had 3 faults
my main bond was one of the faults giving a reading of 4.56 should be 0.05 or below
Next fault was the earthing conductor from the starter at the load side was broken basically you do a r1+r2 test to the top of the starter note it then at...
Thanks for the reply pete999 this makes sense I was questioned on this by someone higher up the chain than myself and did not have a reply but what your makin is sense we are not wanting to test the time clock the circuit it's self so therefore the time clock will not be affecting the circuit in...
Hi guys new to this website just a quick question as it has been a while I have a small 6 way distribution board this only becomes live via a time clock supply wired into it I'm going to be testing this board with a IR dead test on each circuit just to make sure according to guidance note 3 & on...