  1. johnboy6083

    150m submain to multiple outbuildings earthing (PME)

    To add to this, as a rule, don't supply sub boards from an MCB. You won't get full discrimination, and MCB'S have much lower max Zs values than an equivalent fuse.
  2. johnboy6083

    AOV Backup Power

    I've just seen this. Don't forget the principle of an AOV is to maintain the stack effect, to aid in the venting of smoke. If all actuators were to open, the system wouldn't work effectively. It's likely that only one or two floors will open at a time. I've not ever had to design for a...
  3. johnboy6083

    Water heating

    So, E = (mC Dt)/t m = mass in kg C = 4.187 for water @ 10 degrees C Dt = difference between input and output temp. I expect it will be around 55 degrees t = time in secs So for a 180 litre tank, to heat up with 250W will take around 46 hours to heat up (assuming no heat loss) Far too long...
  4. johnboy6083

    600mm swa cable depth rule

    Personally, when I'm specifying projects, I use NJUG 2 as a guide to burial depths of services.
  5. johnboy6083

    It's Earthing Jim, but not as we know it.

    You lot all bitching at eachother sound like a load of birds! ill get my coat ....
  6. johnboy6083

    It's Earthing Jim, but not as we know it.

    I doubt it was installed like that. I suspect fowl play!
  7. johnboy6083

    Emergency Test Switches

    Thats a fair point. It's just the way I like to do it. 3 hours? If a system requires 3 hours worth of lighting, then it's bloody massive. The system should be capable of operation for the expected time of evacuation (worst case scenario of course).
  8. johnboy6083

    Emergency Test Switches

    I personally like to wire the key switches, so that they kill the feed to the standard switches. This allows for a proper test of the system, and lux levels can be checked. I understand however for large office blocks ect, this isn't practical, and they have to be wired so that the standard...
  9. johnboy6083

    Back up generator on domestic

    I personally wouldn't worry about disconnecting the earth, as you're always going to have inadvertent connections via bonding, CPC's and the general mass of earth, between your genny rod, and the DNO earth. In this instance, being a TT system, you needn't disconnect the earth anyway.
  10. johnboy6083

    teaching

    My labourer earns more than that for just turning up, doing as he's asked, and going home!! It's a shame that the money is so crap, because the best people won't apply for the job, as they earn more in industry.
  11. johnboy6083

    Electrical Engineer

    This is no joke, we have a project engineer at work called Roger Hole, he named his daughter Rebecca Constance (R.C Hole) and his other daughters middle name is Heidi! His dog is called Digger! he has a very good sense of humour!
  12. johnboy6083

    Electrical Engineer

    Bens mum was a spark too: Eileen Dover
  13. johnboy6083

    Cables in concrete

    I'd use plastic. It's quick & easy to install and isn't going to corrode.
  14. johnboy6083

    two supplies to a relay

    A control panel doesn't have to abide by BS7671. what I do is cover any terminals that remain energised after operating the isolator with Clear PVC. This is labelled accordingly. this is often done to comply with the form factor requirements of the clients spec.
  15. johnboy6083

    Downloading Microsoft Word?

    The other option is to google 'software for students' if you have a student in your household, then you get massive discounts. This isn't checked though. you could always say you are studying in your own time, from freely available sources. Isnt the definition of a student: somebody who...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock