Recent content by Lenny

  1. Lenny

    3 phase furnace

    36,000 / (400x1.732) = 51.96A. This is your design current (Ib) Select a fuse rating (In) that suits your (Ib) and make sure the tabulated ccc (It) of your supply cable is greater than (In) after any correction factors have been applied.
  2. Lenny

    Howdy

    Yeah, long time ago though.
  3. Lenny

    Howdy

    Morning all Just saying hey....again :cool: used to be an admin on here many years ago but stopped using forums for a long time. Just nosing around, can see quite a few very familiar faces, hope everyone’s well. :thumbsup:
  4. Lenny

    Ring main in 4Core SWA

    Hi. The list below gives the physical CSA of MICC copper sheath when its used as a cpc. Hope it's of use. 2L1 ****** 5.4 mm2 3L1 ****** 6.7mm2 2L1.5 ****** 6.3 mm2 3L1.5 ****** 7.8 mm2 4L1.5 ****** 9.1 mm2 2H1.5 ****** 11 mm2 3H1.5 ****** 12 mm2 4H1.5 ****** 14 mm2 2L2.5 ******...
  5. Lenny

    Limited Company Setup Advice.

    Thanks for the replies. Increased turnover and wanting to remove personal liability due to larger contracts with national companies makes me want to go Ltd now.
  6. Lenny

    Limited Company Setup Advice.

    Hi all. I'm about to start proceedings for creating a limited company. I've not had any real experience nor have any real knowledge of this area and have a couple of questions. 1. When invoicing another company for work carried out, would you deduct say 20% of the total amount and place it in...
  7. Lenny

    PT Connection To Pump

    Sorry for not following up. Turns out the fault was due to airlocking around the PT. The new VSD didn't like the setup so I moved the PT further along the discharge pipework and it worked fine. Thanks for the replies, nothing worse than when you start doubting yourself!!
  8. Lenny

    PT Connection To Pump

    Yes. Starting to think it may be an issue with airlocking around the transducer due to its position as part of the pump assembly. With the loop calibrator connected in place of the transducer, the pump responds as it should.
  9. Lenny

    PT Connection To Pump

    Thanks for the reply. AI2 has been configured in the grundfos go app for pump control via discharge pressure into a private water main. I've taken a 24V supply to the transducer from terminal 8 with the return from the transducer into terminal 7. Screen is connected to gnd. The pump doesn't...
  10. Lenny

    PT Connection To Pump

    Hi all. Could someone please confirm where to connect a 4-20mA pressure transducer to AI2 in the attached photo. I believe it’s terminals 7 & 8 but the pump is not responding at all. Thanks.
  11. ADB920EC-18CB-451A-8FF1-E78CD71E3F43.jpeg

    ADB920EC-18CB-451A-8FF1-E78CD71E3F43.jpeg

  12. Lenny

    Tool tray

    I used to use one of these tool trays, it was made by contico.
  13. Lenny

    Need to buy a multi meter

    Is it an actual multimeter or multifuction installation type tester you're after??
  14. Lenny

    Please help! Boiler ch pump always on!

    We need a bit more info here before we can offer advice. Is it a new system in a new house, does it really 'always' run i.e 24/7 or does it just overrun for a couple of hours, what make of boiler do you have??
  15. Lenny

    distribution board

    By black stub slv do you mean black stub sleeving i.e MICC cable conductor sleeve?? If so, the outer the outer sheathing of the MICC cable is the CPC and tbh, you wont find a lot better even after 30+ years. What problems are you having??

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock