Recent content by mini-si

  1. M

    EICR : Is this a code 2 or not?

    I’m sure I read 16.5 amps enclosed and 19 amps in free air. The conduit drop was only meter at most the rest on tray.
  2. M

    EICR : Is this a code 2 or not?

    Yeh I agree I just think whoever carried out the EICR seen the 1.5mm and thought straight away it’s protective device is over rated with not even giving consideration to type of cable being used. I also agree the RCBO is there to protect the cable and nothing else, appliances have their own fuse...
  3. M

    EICR : Is this a code 2 or not?

    That’s exactly my thought process, another option I was considering was to change socket to a spur to make it a fixed appliance so no chance of anything else being plugged in. Regarding replacing the cable, it’s in a small room back of house which is part office and part store room, which is a...
  4. M

    EICR : Is this a code 2 or not?

    Over rated protective device for cable size. 1.5mm on 16 amp radial which I normally wouldn’t question, however with it being FP cable thought I’d pose the question to you guys.
  5. M

    EICR : Is this a code 2 or not?

    Yep, single socket. This was my thinking. Although not a fixed appliance and one could say that an extension lead could be plugged in causing over load, but where the socket is located fixed behind a big heavy grease trap unit which is in turn fixed to stainless catering equipment the chances of...
  6. M

    EICR : Is this a code 2 or not?

    This is a EICR that has already been carried out by another contractor and we get the remedial works following the test. I have now installed a fused spur next to the board to protect the cable, but I was almost certain that fp could carry the current rating of the protective device feeding it...
  7. M

    EICR : Is this a code 2 or not?

    hi all, Ok let’s get straight to the question. Is the below a code 2 defect on a EICR?? A 16amp bs61009 supplying a single 1.5mm FP200 cable with a run of approximately 8 meters, which is feeding a IP rated single socket for a grease trap unit. The socket is low level behind the grease trap...
  8. M

    Safety shut off valve for boiler??

    Lovely guys, great advice from you all, superb forum this. Getting to chat with guys from all asspects of our trade. Only been a sparks for 10 years so as the saying goes. You learn something new every day
  9. M

    Safety shut off valve for boiler??

    It's not a fcu feeding it, it's a old memshield metal clad isolator with old bs3036 rewireable fuse as the protective device.
  10. M

    Safety shut off valve for boiler??

    Short circuit, nicely put. Thanks for your advice. The heating scene is new to me but am finding it very interested.
  11. M

    Safety shut off valve for boiler??

    It might well be that it needs a emergency stop installed thinking about it! a inspection was carried out and picked up on the points listed in my first post. I am more than likely swaying towards the emergency stop although there is a isolator 0.5meters away from the boiler. Was just seeing...
  12. M

    Safety shut off valve for boiler??

    Any advice at all guys??
  13. M

    Safety shut off valve for boiler??

    Hi all, had a call out friday afternoon to assist a gas engineer to a boiler not working in a bank. Job was to: - get boiler working- DONE - sleeve main Gas pipe through floor- being done tomorrow - install bonding to Gas meter- DONE - install SSOV to boiler ??? The boiler is rated...
  14. M

    JIB Electrotechnical Certification Scheme (ECS) Need to get my JIB card, but need some help first guys!

    Have just read that myself on JIB site.lol thanks Tom, will call them tomorrow.
  15. M

    2931 Exam tomorrow, tips for next 24hrs

    ask for scrap paper when you get there and as soon as the exam starts write down any calculations you have remembered, that way your not under pressure to remember should you need to. We can all make mistakes under pressure. Hope all goes well for you tomorrow mate, good luck.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock