Yeh I agree I just think whoever carried out the EICR seen the 1.5mm and thought straight away it’s protective device is over rated with not even giving consideration to type of cable being used. I also agree the RCBO is there to protect the cable and nothing else, appliances have their own fuse...
That’s exactly my thought process, another option I was considering was to change socket to a spur to make it a fixed appliance so no chance of anything else being plugged in. Regarding replacing the cable, it’s in a small room back of house which is part office and part store room, which is a...
Over rated protective device for cable size. 1.5mm on 16 amp radial which I normally wouldn’t question, however with it being FP cable thought I’d pose the question to you guys.
Yep, single socket. This was my thinking. Although not a fixed appliance and one could say that an extension lead could be plugged in causing over load, but where the socket is located fixed behind a big heavy grease trap unit which is in turn fixed to stainless catering equipment the chances of...
This is a EICR that has already been carried out by another contractor and we get the remedial works following the test.
I have now installed a fused spur next to the board to protect the cable, but I was almost certain that fp could carry the current rating of the protective device feeding it...
hi all,
Ok let’s get straight to the question.
Is the below a code 2 defect on a EICR??
A 16amp bs61009 supplying a single 1.5mm FP200 cable with a run of approximately 8 meters, which is feeding a IP rated single socket for a grease trap unit. The socket is low level behind the grease trap...
Lovely guys, great advice from you all, superb forum this. Getting to chat with guys from all asspects of our trade. Only been a sparks for 10 years so as the saying goes. You learn something new every day
It might well be that it needs a emergency stop installed thinking about it! a inspection was carried out and picked up on the points listed in my first post. I am more than likely swaying towards the emergency stop although there is a isolator 0.5meters away from the boiler.
Was just seeing...
Hi all, had a call out friday afternoon to assist a gas engineer to a boiler not working in a bank.
Job was to:
- get boiler working- DONE
- sleeve main Gas pipe through floor- being done tomorrow
- install bonding to Gas meter- DONE
- install SSOV to boiler ???
The boiler is rated...