Cheers Lee,
Trying to make it work but stepping back, your comments have clarified my doubts that this wasn't suitable!
Their 'heating engineer' supplied the RF3 & will get it back!
Good to have a heating guru around!
Thanks,
Rob
Hi,
Since getting back into the trade a few years back have installed controllers for boilers with room stats etc & the odd new S plan system - infrequently & admit I am not well versed in heating controls though can follow a circuit diagram!
Customer has asked me to install a Drayton digistat...
Thanks guys for all your input - great resource here.
Big thanks to Marconi for his detailed explanation & solution - hager RCBO sorted it.
Very useful to know for the future.
Rob
Hi,
No update as Bosch have only just sent an engineer and have been recovering from a carpel tunnel op - apologies.
Bosch will only say a class A RCBO Might solve the problem - difficulty being there was only room for a 4-way board in the small meter cupboard & I can only find double pole...
Appreciate everyones input.
@Murdoch
Said socket tests satisfactory - renewed it anyway.
As well the normal tests plugged in a 2.5 KW heater which had no issues.
Basically when on a short radial circuit hood trips -whether on short leg of ring or ccu socket (cooker circuit approx same length).
@Richard
Yeah, pretty straightforward now at home - straight 2M run to board = trip, longer run = no trip.
Would open hood up but will leave it I think until Bosch have had a look.
These faults are sent to test us lol.
yeah, I know mate. So as above replaced short leg 2M with IR tests of > 900 Meg - no other circuits connected in board.
Duplicated fault on cooker ciruit with similar length.
So if the longer leg is absorbing 70mA it doesn't compare with other faults I have dealt with such as leakage on a long...
MFT calibrated - EL clamp meter six months old. RCBO's ramp tested (25mA -27mA) Even though RCBO's were new swapped for new ones.
Murdoch - I'm looking believe me but trying to understand the science behind it.
@Richard - was thinking along those lines though I'm not aware of the method to prove this theory - ring circuit tests were r1 0.63 rn 0.57 & r2 0.97 - average 2 bed bungalow so around 80 square meters.
Trouble is I know when the Bosch engy comes out he will say it works on one socket so must...
Clamped the fan CPC via a stripped extension lead & got same readings - fine when connected to a longer circuit but spikes when fan speed increased on short leg.
Hi,
Well disconnected all other circuits and was testing from a 2M run 2.5 T&E that is the first leg of the ring to the socket for the hood - even replaced this piece of twin (even though previous tested fine) & replaced single socket. Done the same again with the socket on the CCU with only...
Hi,
Been back in the trade a few years now & a regular lurker here (236 I & II & C, 2391, time served etc, 17th) - I have always managed to track down answers using the search however need some help on this one.
New kitchen install in a 2 bed bungalow involving a board swap to RCBO's as only...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.