thanks that makes a lot more sense RE TP no neutral and net currents.
It’s a contactor for a 3P&N heater, it would be hardly any extra effort to route the neutral through the enclosure I was just wondering if (and why) it was needed as I couldn’t find anything on google regarding a circuit that...
It’s a 32a supply, there’s 3 of them through 3 separate contactors .
I could use a 4 pole contactor or route my neutral through it I’m just asking if it’s necessary?
From my understanding eddies occur when the lines and neutral go through different holes, so if there is no neutral required...
I have to supply a 3 phase + neutral circuit but I have to run it through a contactor. The contactor is 3 phase no neutral and will be bushed onto the left side of the board with 2 bushes (one for feed, one for load).
The other side of the board is bushed onto some trunking where the load will...