Recent content by Tubecatgs

  1. T

    3 wire sub panel only 2 120v outlets

    Thank you... darn. It doesn't look like you can modify the breaker to accept a larger neutral wire.. if that scenario did work, would you still bond the neutral and ground (since their is a GFI at the main panel)? Next question or option, to make sure their is a ground back to the service...
  2. T

    3 wire sub panel only 2 120v outlets

    A friend of mine has a detached garage (200 feet from the house/service panel) with a newer Square D 100 amp Homeline sub panel that was never hooked up. Running to the sub panel from the service panel are only (3) 6 gauge aluminum (Erskine I think they call it) direct burial wires. I think...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock