  1. F

    IR short, only when cable connected?

    Have you got the main switch on ? If so then you need to disconnect the neutral from the neutral bar.
  2. F

    Voltage drop help please

    Hi helio007 , I think they have used a different calculation but your answer would also be right. They seem to have used the 0.15 value, 0.15 x 60 x 1.2 (70 degrees ) = 10.8v,
  3. F

    SWA r1r2 35mm ... .....

    Hi , if you use the resistance values from cable manufacturers like Batt cables then the resistance of 35mm is 0.524 and the resistance for the armouring is 2.1 . So 160 x 0.524 x 1.2 (70 degrees ) /1000 =0.10 160 x 2.1 x 1.18 (60 degrees ) / 1000 = 0.39 therefore 0.10 + 0.39 = 0.49
  4. F

    why bother in the first place

    Was the fault on the ground floor ring due to the neutral bar being linked ie as soon as a load was put onto the ring then the rcd tripped. Has the circuit ever worked ?
  5. F

    why bother in the first place

    Where does the third neutal from the main bar go. Does it feed the third neutral bar and bypass the rcd?
  6. F

    Strange RCD Problem

    Have you carried out your insulation resistance tests with the cpc connected to the means of earthing. Your line conductor may be shorting to a piece of earth metalwork.
  7. F

    Niggling bad feeling.

    Code 3 for lack of rcds , recommend either rcbos to sockets and showers or fit dedicated rcd sockets to ground floor flats where they can supply anything for use outdoors. The regs are not retrospective.
  8. F

    Trailing edge or Leading edge for LED downlights?

    You could use an MK 1523WHILV which looks like a normal white dimmer but is capable of dimming LEDs at min 4w and max 70w. Have done a few and have had no probs. Before that I used to use a 1000w Varilight dimmer which worked very well.
  9. F

    16mm or 6mm

    I have had this discussion with a BC inspector before I was able to self notify and he assured me that if the DNOs earth is sweated on then it is the suppliers responsibility. I had the case of what looked like a 4mm bare piece of cable sweated on . I kept this as short as possible and...
  10. F

    Ring Main Tripping RCD, Line to Earth reads 0

    Hi chaps , first post so hello to everyone. One explanation could be a neutral to earth fault and the tester is picking up a reading through the connected load. Not all switched spurs are double pole and can leave the neutral connected in which case if there was a neutral to earth fault then...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock