J
junior tech
good day guys,
I badly in need of your comments with regards to electrical protection system. The issue took a place when we tried to run a motor with rated power of 600 KW, 13.8 KV and rated current of 30 Amps. This motor fed from ABB switchgear with tow incomers and normally closed bus tie between. What happen is when the motor received start signal, the main incomer which motor connected to has tripped along with bus tie causing all other equipment to trip as well. When motor's feeder events been checked, it shows that the motor tripped due to instantaneous over-current around 2900Amps which is very large value. And the main 13.8KV incomer’s events show that the vacuum circuit breaker VCB open due to under-voltage with differential relay of bus PT activated too. I’d reviewed the protection set points of both motor feeder and main incomer. Motor over current set point is 7.6 times motor rated current with time delay of 0.05 second, incomer set point of under-voltage low and high respectively 80% and 90% of rated voltage with time delay of 3 seconds for both high and low settings. My concern, why did the incomer and bus-tie open? Is it because motor draw high current and cause under-voltage at main incomer? If yes, so why did it open before the period of its time delay completed since the over-current was instantaneously?
Please I need a your experience to clarify this issue…. Thanks
I badly in need of your comments with regards to electrical protection system. The issue took a place when we tried to run a motor with rated power of 600 KW, 13.8 KV and rated current of 30 Amps. This motor fed from ABB switchgear with tow incomers and normally closed bus tie between. What happen is when the motor received start signal, the main incomer which motor connected to has tripped along with bus tie causing all other equipment to trip as well. When motor's feeder events been checked, it shows that the motor tripped due to instantaneous over-current around 2900Amps which is very large value. And the main 13.8KV incomer’s events show that the vacuum circuit breaker VCB open due to under-voltage with differential relay of bus PT activated too. I’d reviewed the protection set points of both motor feeder and main incomer. Motor over current set point is 7.6 times motor rated current with time delay of 0.05 second, incomer set point of under-voltage low and high respectively 80% and 90% of rated voltage with time delay of 3 seconds for both high and low settings. My concern, why did the incomer and bus-tie open? Is it because motor draw high current and cause under-voltage at main incomer? If yes, so why did it open before the period of its time delay completed since the over-current was instantaneously?
Please I need a your experience to clarify this issue…. Thanks