Hi folk’s adiabatic equation, help / advice
S = Size of earth bonding conductor required.
I = pfc in amps.
t = disconnection time in seconds.
K = values in table 43.1.
I am trying to work out if a 6mm main earth is adequate on a TN-C-S system
Is the 6mm cpc in the 16mm T&E allowed?
Have been asked remove and upgrade / a DB in a flat supplied by a 16mm T&E on a 60A switch fuse BS1361.
Already present from flat DB 10ml to gas and water
or would you go with table 54 .7 s = mm2 if the protective conductor is of the same as the line conductor ?
but it must have been able to carry the fault current as acpc???
Zs @flat 0.16
Pfc 1.85ka
Thanks in advance guys