Hi all

I would like a bit of advice to do with a DOL starter ill be fitting. Basically I'm replacing an old water damaged crabtree DOL starter with a new mcg DOL starter. The old coil was pulled in via a single channel heating timeclock and the new one will need to be too. The old DOL just had a reset button where the new stuff has start and stop buttons. Im super rusty on DOl starters and the like as ive not done any for absolute ages and none operated via timeclock. My main question is, is there a way to connect the new DOL so that the heating timeclock makes and breaks the contactor to operater the 3 phase pump? Attached are pics of the new and old gear. Thanks
 

Attachments

  • 16083251636064774597981942799857.jpg
    275.8 KB · Views: 19
  • 16083251798153246416331140272240.jpg
    317.3 KB · Views: 16
Hi all

I would like a bit of advice to do with a DOL starter ill be fitting. Basically I'm replacing an old water damaged crabtree DOL starter with a new mcg DOL starter. The old coil was pulled in via a single channel heating timeclock and the new one will need to be too. The old DOL just had a reset button where the new stuff has start and stop buttons. Im super rusty on DOl starters and the like as ive not done any for absolute ages and none operated via timeclock. My main question is, is there a way to connect the new DOL so that the heating timeclock makes and breaks the contactor to operater the 3 phase pump? Attached are pics of the new and old gear. Thanks
What voltage was/is the coil?
 
The timeswitch is unlikely to be rated to switch 400V, therefore it would be normal to use a starter with a 230V contactor coil, but as per Pete999's comment you must check where the coil is supplied from (the pump circuit or a separate control circuit) and at what voltage.

For automatic control you can't use the start and stop buttons so disconnect those and the contactor's N/O holding contact.
If the coil supply L & N both come from the timeswitch simply connect L via the O/L relay N/C contacts 95/96 to the coil A1, then A2 back to the timeswitch N. If the control supply is taken from the pump circuit then the L would go via any control fuse - timeswitch contacts - 95/96 - A1.

Set the O/L reset to manual so that it doesn't keep restarting in the event of a fault and dial in the FLC.
 
You have obtained the wrong starter. Your system essentially has an automatic remote control in place of the green button start facility. As opposed to doctoring the one you have which could lead to confusion you need the correct starter with correct coil voltage.
 
The timeswitch is unlikely to be rated to switch 400V, therefore it would be normal to use a starter with a 230V contactor coil, but as per Pete999's comment you must check where the coil is supplied from (the pump circuit or a separate control circuit) and at what voltage.

For automatic control you can't use the start and stop buttons so disconnect those and the contactor's N/O holding contact.
If the coil supply L & N both come from the timeswitch simply connect L via the O/L relay N/C contacts 95/96 to the coil A1, then A2 back to the timeswitch N. If the control supply is taken from the pump circuit then the L would go via any control fuse - timeswitch contacts - 95/96 - A1.

Set the O/L reset to manual so that it doesn't keep restarting in the event of a fault and dial in the FLC.
Thank you, this makes sense. Much appreciated
 
You have obtained the wrong starter. Your system essentially has an automatic remote control in place of the green button start facility. As opposed to doctoring the one you have which could lead to confusion you need the correct starter with correct coil voltage.
Thank you
 

Reply to DOL Starter advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all From the outset I'm not in an electrician. I am posting here because I'm thinking the subject matter is quite specific and will prob...
Replies
43
Views
6K
Hi all. I'm looking to build myself a rig with a small single phase motor and learn a bit more about motor controls etc. I mostly do domestic and...
Replies
34
Views
3K
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock