T

Tiden Elec

Hi I have a 3 phase 400v motor wired in star configuration it is controlled via a 3 pole 415v coil contactor which is switched simply via a stay put stop ... In for off Out for run.. ( Spanish design ) there is also a single phase fan connected between one phase and the star point of the motor. Got a number of these machines like this but this one.... sometimes when you release the stop button to start the motor it runs in reverse !!!!
In 50+ years in the industry Ive never seen this happen .... Any ideas?
Thanks
Dennis
 
I wonder if there is a phase missing or a faulty contactor. The missing phase possibly being replaced by the single phase motor.
 
  • Like
Reactions: Inteificio
I'm assuming that you've done all the usual supply polarity / rotation checks?
 
Agree, likely intermittent contact or connection in one phase. If the fan is disconnected it probably won't budge, but with the fan there is enough of a phase-shifted current flowing to generate a modest starting torque. Presumably it doesn't have much load at start-up?

Clamp ammeter on each line in turn to spot the one that doesn't always have load.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3 phase motor reversing itself
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
Tiden Elec,
Last reply from
Lucien Nunes,
Replies
3
Views
1,873

Advert