The OP said he has a plastic pipe entering the garage. Not copper
So to test the plastic pipe you would disconnect your copper part and then test to MET, which would then give you a reading of ?? Remember it's plastic!
all depends on the conductivity of sh!te.
An update, went back to site today for something else and the plumber has been at work. The sink as been replaced with a stainless one and its attached to the concrete wall. I repeated a test between the boards earth and the sink and got 700ohms - I'm presuming one of the screws has got the rebar.
So I could put a 6mm conductor between the board and the pipe (which is bigger than the supply conductors) - however this isn't a main protective bonding conductor as its not continuous
The other option is suppose it to stick in an earth rod and go TT but that's a right PITA.
Any thoughts?
One reason why you ALWAYS test and never assume that copper pipework after a plastic incomer isn't carrying an extraneous earth potential... Just hook up a pipe clamp to the copper pipe section, you can bet your last pound, it'll be providing better protection than a typical UK TT system will!! lol!!
Unless it was you that put the spikes in
Boydy