bailes1992

I've just moved into a new house, It's a 4 year home built by a major developer. The previous couple who lived here were non-diy savvy and from speaking to them on numerous occasions the only work done on the house was decorating and flooring which they got people in to do.

Now, the house has Crabtree accessories which I personally think are unsightly and have yellowed over the last few years even through nobody has smoked in the house. So, I'm currently going around changing them out for Hager items and making a few minor alterations.

I have an external single garage. It is fed by a 6mm² T&E to a double back box in my dining room. In the back box there is a set of connectors where it joints onto a 6mm² 3 core SWA which goes into the garage. I can't see any ducts and the cable appears to be directly in the ground. While I was swapping out accessories I decided to change the blank plate on this back box and found this...
http://i.Upload the image directly to the thread.com/7LZeKwG.jpg?3
http://i.Upload the image directly to the thread.com/hY5PUL8.jpg?2


So no earthed armouring, no earthed back box and no earth tape on the black conductor of the SWA. Now I must admit I've seen a lot worse, but I'm quite annoyed that you buy a new-ish house with a copy of the EIC and come across something like this.

Now, regardless of the fact this doesn't meet BS7671 522.8.10, I thought this was downright lazy and of course I couldn't leave it as it was.

https://i.Upload the image directly to the thread.com/CtEbUX8.jpg

No my tidiest job but I managed to gland the cable off in the wall which left me with very grazed knuckles. I've used a serrated washer on the back of the SWA gland to ensure good continuity between the gland and the back box and I've obviously earthed the back box.

Now there's the issue of the hole I cut in the wall. The house is dot and dabbed so it's a simple case of cutting in a new piece of plasterboard, gluing it in with dry lining adhesive and a light skim of filler. The issue is my Wife who has said if it was such an issue, surely I should get the contractor back to fix or at least pay to fix the mess and she wants me at the bare minimum to contact the NHBC.

Now, would you just fix this yourself and leave it where it was or would you get others involved to pay for the costs of repair?

The only other interesting thing is there is a 30mA RCD in the garage despite the garage being fed from an RCD protected section of the CU in the house. o_O
 
I think id have just earthed the armouring at the garage end and not hashed up my wall

I agree with you to a point but I've always been of the opinion that it's best practice to earth the SWA at the start and not the end. Ideally the SWA should be earthed at both ends which I will eventually do. My garage is being turned into a mini workshop so I will be installing a new single phase CU and installing a run of 50x50 galv trunking around the perimeter with galv conduit drops.
 
I suspect it would be you versus a mighty wall of indifference. However, should you write to NHBC, I would love to know their response! This is the tip of a rather large iceberg. Thanks
 
Unfortunately this is not a rare sight. It is a bit quicker to do it incorrectly so some folk (being polite) do it. Perhaps think about Wago style connectors to get all the earths together without being in series :)

IMG_1021.jpg
 
Don't waste your time contacting anyone.
They won't be interested.

Had there have been an injury they might have been.
 
  • Agree
Reactions: robd and Tes369
Presumably the contractor doing the installation did the EIC? You could flag it with which ever scheme they’re with and see if there are any SM review spots you can highlight it on. Otherwise don’t waste your time and sit back knowing that you’ve sorted it :cool:
 
Not worth contacting the NHBC they won't be interested unless you pay them to investigate it if they uphold your complaint your costs should be refunded by the builder.
Chance of success is minimal, looked into making a complaint some years back and research suggested the money would be better spent on the repair than the complaint after all the NHBC is owned by the buiders
 
  • Agree
Reactions: Des 56 and Rpa07
I am afraid it is caveat emptor when purchasing a house. Any defect not picked up during a survey (you did have a survey?) may be actionable depending on what level of survey you had. However I doubt this would be covered by a survey as most take the cheapest option survey. So whatever defects you have inherited are yours to deal with.
 
  • Like
Reactions: a-z electrics
I think id have just earthed the armouring at the garage end and not hashed up my wall
That was exactly my first thought on looking at the pic, before I saw your post!
 
get the tin out.
shopping
 
i'm just waiting for lego to up their game and make their blocks 18" x 9". good insulation value and no need for bodgit the builder. all homes could then be self-build. "click and go".
 
Why do you lot keep doing this to me? Bringing up the problems with "new-builds"?
You KNOW I hate them!!!!
Yes, Murdoch...unskilled people throwing them up.....
Oh, I need to lie down....
 
Just saw a clip on the news about a brick-laying robot.
Is the writing on the wall for sparkies?

 
  • Like
Reactions: ferg
I want the word caveat banned from the forum:D
 
You're lucky it's 6.0mm most new builds have only 2.5, when I used to work for a company that did new houses we took the T& E outside to an IP box to convert to SWA.Although not textbook if the other end was soundly made off using gland and preferably earthnut wouldn't of worried.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Found this in my 4 year old house...
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
64

Advert

Thread statistics

Created
bailes1992,
Last reply from
EalingBadger,
Replies
64
Views
7,209

Advert