Doing an EICR earlier and got some wierd readings not experienced before, thankfully property is empty.

I did a Zdb on a TNC-S system and got an earth loop of 0.44 this was with all earths connected at the MET in the DB so I checked the main earthing conductor into the cut out in the outside meter cabinet and all was ok, nice and tight, so I then disconnected the main earthing conductor in the DB and tested the Ze which measured 0.38 still above max.

As I put the main earth back into the MET I got a little bit of arcing o_O, so with test leads I measued between the MET and main earth and got 40V!!!!!!! I also got 39V reading between N & MET.

Going back tomorrow for further investigation, but any ideas out there?
 
Well theres likely a fault to earth (or general leakage from some equipment) and with you having the earth dissconnected with the installation live (???) it's got nowhere to go. Contact dno about high ze though, from experience I doubt they'll do anything though
 
Did you isolate the installation before disconnecting the main earthing conductor?
 
so I then disconnected the main earthing conductor in the DB and tested the Ze which measured 0.38 still above max.

As I put the main earth back into the MET I got a little bit of arcing o_O, so with test leads I measued between the MET and main earth and got 40V!!!!!!! I also got 39V reading between N & MET.

What maximum is that above? There is a nominal value of 0.35 but this isn't a maximum.

Apologies for the stupid question but did you confirm that the installation was isolated before disconnecting the earthing conductor? There must be a source of voltage connected to cause this, but with the installation isolated that should be impossible.

The neutral and earthing conductor are joined together in the cutout so yes you will get the same voltage on each one.
 
[/QUOTE]There must be a source of voltage connected to cause this, but with the installation isolated that should be impossible.[/QUOTE]

The voltage was between the TN-C-S earth (or neutral, same thing) and the DB earth, which may be in contact with local true earth. So the source of voltage might actually be the PEN of the supply sitting rather high, with current flowing back to local earth when connected. 40V is a bit high though so until confirmed by the OP I won't speculate on whether the installation was properly isolated.

Nonetheless, a highish Ze on a TN-C-S would tally with a highish voltage between PEN - local earth under typical distributor load.
 

Reply to High Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
786
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
743
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock