Discuss Hot tub electric shock in the UK Electrical Forum area at ElectriciansForums.net
Based on that then it can only be the supply earth that's causing the issue. I agree with your brother. Disconnect the supply earth and see if "tingle" disappears.That will confirm it.
I think for this one I will just stick with the multimeter results rather than doing the finger test ? thankyou for the help is much appreciated
I would never install a hot tub on TNC-S. My own are on a genuine TNS system, and use the DNO earth, but if it were TNC-S, the tubs, and the buildings by them, would be TT.
More and more I am thinking all hot tubs should be on a TT supply, as even if your supply appears to be TN-S there is a chance that elsewhere repairs or cable replacement has essentially converted your supply to TN-C-S (just a rather long 'S' there).
And now we come to the nub of the problem. An unsatisfactory supply system. TNS was and is the only proper supply system. Ironically I thought that a combination of outside metalwork like heat pumps, electric gates, electric vehicles etc would highlight the frailties of TNC-S. But I now wonder if it may be hot tubs that eventually highlight the issues!!
By "genuine TNS" I mean that I can see all the earthing rods, and every inch of the supply cables, all the way from the 11kV - 230-0-230 Tx, to all three DNO service heads
Then as pc1966 states you have truly a unique situation. Can I enquire about the earth rods? TNS is the one supply's system I have never worked on. What is the earth electrode arrangement?
Reply to Hot tub electric shock in the UK Electrical Forum area at ElectriciansForums.net
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
I experienced an electrical shock while replacing an A/C Fan Coil's 120vac, single phase motor that was above the ceiling grid in an office, while...
4K
I have an inground pool with a 22 year old, 120vac light fixture in a niche connected to water-holding conduit running to a switch in an...