L

Lee Gold

I have sockets in my room but how do I test if it's ring or radial because I want to add another socket
 
a ring will have 2 Live cables in the MCB. with all L's, N's and E's of the circuit dissed.check for end-end continuity.
 
  • Like
Reactions: 1 person
Also be aware that if it is a RFC then there is the possibility of spurs being present on the circuit. Have a look in Appendix 15 of BS7671. :)

If i was adding points to a RCF i would always try and keep it a Ring rather than spur.
 
Last edited by a moderator:
Was in an older 3bed house a few months back, no lables on CU
turned out each of the 3 bedrooms had their own radial circuit, one circuit in it's own 16A MCB and the other 2 connected in another.

I went away thinking, you can assume nowt without a good old nose around.
 
Was in an older 3bed house a few months back, no lables on CU
turned out each of the 3 bedrooms had their own radial circuit, one circuit in it's own 16A MCB and the other 2 connected in another.

I went away thinking, you can assume nowt without a good old nose around.

That is only 2 circuits as a circuit is defined by the ocpd not the number of conductors connected to it
 
That is only 2 circuits as a circuit is defined by the ocpd not the number of conductors connected to it

I agree with what you said, I know it to be true. :vanish:
I think the point I was making is I foolishly thought is was 1 Ring FC at the time.
 
I agree with what you said, I know it to be true. :vanish:
I think the point I was making is I foolishly thought is was 1 Ring FC at the time.

Why did you think a 16A MCB had a ring connected to it?
 
I’ll be straight with you Dave, sheer ignorance !
I saw 2 2.5mm2 brown cables coming out of the top of an MCB and thought Ring FC. :lol:
 
Oddly on one house I went to that had been "sorted out" electrically at great expense to the owner, I found that both "rings", that were non continuous, had been "fixed" by putting them on 16A breakers.
So there were two conductors in each breaker and if they had been correctly installed would have been ring finals.
Whilst admittedly this is possibly safe, I did feel that solving the underlying problem would have been better.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
How do you test for ring or radial?
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
Lee Gold,
Last reply from
Richard Burns,
Replies
9
Views
146

Advert