Hi Guys,

Just a quick one, on a power rewire is it acceptable to wire new cables under floor and join onto old legs of circuit but only from socket to underfloor. So only about a foot of existing cable left in to stop damage to walls.

Thanks
 
It depends on whether the old cable tests out ok and whether you have permission to leave old cables in thus making it a partial rewire of that circuit
 
as i understand it, you want to use the old cable in the walls to avoid chasing in new. if you do this :

1. old cables need to give a good IR reading.
2. your joints under the floor need to be maintenance free, i.e. crimp and heatshrink or wagos in enclosures.
3. 2 colour sticker on CU, if applicable.

however, although you can make this idea comply with BS7671, joints should be avoided wherever possible.
 
Hi Guys,

Just a quick one, on a power rewire is it acceptable to wire new cables under floor and join onto old legs of circuit but only from socket to underfloor. So only about a foot of existing cable left in to stop damage to walls.

Thanks

That sounds like a lot of joints ? What was wrong with the original cables?
 
not necessary to rewire just because existing cables don't match the new stupid colour code.good point.
 
Hi Guys,

Just a quick one, on a power rewire is it acceptable to wire new cables under floor and join onto old legs of circuit but only from socket to underfloor. So only about a foot of existing cable left in to stop damage to walls.

Thanks

Surely your making more work for yourself this way, and if you don't crimp tightly enough they come away your liable why not just take the plunge and chase the cables into the walls or will customer not let you?

Also if your needing to rewire surely the customer expects a little bit of damage to the walls
 
As Tel.....joints to be accessable (unless maintinence free)....but i would say that if a customer wants a rewire then thats what they should get ....leaving old cable/s as part of the job dont constitute a full rewire to me......maybe the customer dont want walls damaging by chasing etc but they should think about that before ordering the work............
 
one of the best ones we found once was how the "competent person" had cept the vir both legs from the board and joint boxet it onto pvc for the ring....no cpc...nowt........competent person...my ar$e.....
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Is this acceptable?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
Sjn electrical,
Last reply from
hercule,
Replies
10
Views
1,355

Advert