paddyc3112

Hi,

I have been asked to install 2 extra magnetic fire door closers to an existing system. I was just wondering if these have to be wired back to the fire panel or can they be fed from an existing local magnetic fire door closer?

Any help would be very appreciated.

Ta.
 
If the existing magnetic doors are controlled by the fire alarm, then you can connect the new doors to the existing circuit.
24v door holders draw 50mA, and 240v draw 20mA....so good idea to check existing power supply or feed
 
Yeah, its not a major question at all is it?
With a set of original fire doors in place, and hopefully connected to the fire alarm...... a interface & psu for addressable or wiring back to the panel conventional, will not be required.
 
Hawkmoon/camerabloke I will look into this. If it is a conventional system, can I not spur from an existing magnetic door? Or should I run it back to the panel?
 
if the existing doors are already interfaced into the fire alarm system, then the is no reason why you cannot spur off existing doors. Conventional or addressable..
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Magnetic fire door closers
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
paddyc3112,
Last reply from
paddyc3112,
Replies
9
Views
1,965

Advert