I have a 2.5mm supply in a loft and from this i have it going to a FCU which I then have my lighting mains for a switch coming from the load side of FCU , I then go from the FCU to 4 different sockets and then last in line I have to connect to another FCU for the bathroom heater downstairs , is this acceptable? (This would be a radial circuit as only one leg up from board for supply )
 
So long as it’s CPD is 20A and you meet disconnection times that sounds fine.
 
Sorry are you meaning my Circuit breaker should be rated to 20A as I was planning on using existing 32A breaker but can change to 20A if necessary
 
Pg 188 of the OSG refers - max CPD on a 2.5mm radial is 20A due to the cable only being rated to 27A.
 
  • Like
Reactions: pc1966 and DPG
Pg 188 of the OSG refers - max CPD on a 2.5mm radial is 20A due to the cable only being rated to 27A.
NB - you said 'loft' in your OP which implies insulation, so check your derate factors as well!! It's 27A at method C, not buried throughout in itchy-scratchy stuff.
 
  • Like
Reactions: pc1966
Yes there is plenty insulation up the loft as is with most lofts but my cables are clipped to the top of the joists as floor in new loft is being raised so think I should be okay as cable not directly buried in any insulation.
 
  • Like
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Multiple FCU on radial?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Electrician1972,
Last reply from
Electrician1972,
Replies
8
Views
3,147

Advert