Discuss Multiple FCU on radial? in the UK Electrical Forum area at ElectriciansForums.net
I have a 2.5mm supply in a loft and from this i have it going to a FCU which I then have my lighting mains for a switch coming from the load side of FCU , I then go from the FCU to 4 different sockets and then last in line I have to connect to another FCU for the bathroom heater downstairs , is this acceptable? (This would be a radial circuit as only one leg up from board for supply )
So long as it’s CPD is 20A and you meet disconnection times that sounds fine.
Pg 188 of the OSG refers - max CPD on a 2.5mm radial is 20A due to the cable only being rated to 27A.
NB - you said 'loft' in your OP which implies insulation, so check your derate factors as well!! It's 27A at method C, not buried throughout in itchy-scratchy stuff.
Reply to Multiple FCU on radial? in the UK Electrical Forum area at ElectriciansForums.net
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
I found a 13A FCU, connected to the kitchen ring supplying an outdoor junction box, providing two SWA 2.5mm radials. Unconventional? yes. One...
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Hi everyone. Im new here... I need advice on wether it is safe and okay to have 3 × 13amp fcus on its own radial with each having single socket...
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...