I was initially intending on a 63A RCD but one of my questions was if that would be enough which is why I was asking if a 100A would be acceptable but I have not been able to find a 100A RCD

Putting the whole board on an RCD is a bad idea, the aircon units will very likely be tripping it quite often.

I'm not convinced by your plan of putting them on RCBO's either, why do they need rcd protection?
[automerge]1587372362[/automerge]
Yes, that is correct. So each one of the aircon circuits will be on an rcbo but are you saying that the circuit going from existing board to new one needs more protection than just a 100A main switch? Do you think a 63A RCD would be enough?

I also thought about installing a Henley block and then I would just have the main incoming going to both boards.

With regards to the Henley block option, would I need to install an isolation switch before each board or can I run the tails direct to the DB

You need to explain this a lot better than you have, you've talked about splitting the tails in a Henley block, and about a three phase supply elsewhere.
Is this board being located at the incoming mains position, adjacent to an existing DB fed by a submain or is the new DB remote from all other DBs and itself fed from a submain?
 
4 X a/c units off one 30mA RCD no matter where you put it is bad design is likely to create nuisance tripping. individual RCBOs or MCBs are the way forward depending on your wiring from the board to the outdoor units.
As the garage is single phase then you need to clamp this phase at the 3 phase board and see what the load is one this phase first before banging 4 X a/c units in. You may need to jiggle a few single phase loads in the 3 phase board to get a best guess balance out of all three. They dont need to be perfect but you do need to do a max demand calc to ensure you are not hammering one phase.
 
The "least trouble" option is to feed the new DB from a 63A MCB in the existing board, and then put in separate MCB for each A/C unit, or RCBO if the A/C units have any need for additional protection (cable routes not guaranteed deeper than 50mm behind wall surface, etc). For the minimal extra cost I would go RCBO.

You won't get much selectivity between the A/C final breakers and the 63A feed, but making it 63A C-curve or D-curve would help, and also checking what the A/C specifications say they really need in order to select the smallest acceptable MCB/RCBO as well.
[automerge]1587380129[/automerge]
As already said, the A/C capacity is it heat-pumping ability and typically the input electrical power is less than half of that, but they do have motors starting and stopping so you might find the breaker specification is higher to allow for the surge.
[automerge]1587380353[/automerge]
Final thought, have to checked the feed arrangement to the garage DB you are planning on attaching to? You need to check the sub-main cable has both the necessary current carrying capacity AND low enough impedance to meet the voltage drop requirements.
[automerge]1587380462[/automerge]
A photo might help!

Reading the OP again it might be the mains supply enters at the garage, so no sub-main cable rating to worry about there, but the issue of looking at how the per-phase loads stack up still needs to be done.
 
Last edited:
Get a link kit that connects to the busbar or 100amp terminals that connect to the bus bar, tail off less than 3 meters into a switch fuse isolator, then from isolator to a DB containing your A/C circuits. Perhaps go polyphase and fit a 4 way DB as not to overload any one phase
 
Get a link kit that connects to the busbar or 100amp terminals that connect to the bus bar, tail off less than 3 meters into a switch fuse isolator, then from isolator to a DB containing your A/C circuits. Perhaps go polyphase and fit a 4 way DB as not to overload any one phase

The tails length would need to be less than 3m total from consumers terminal if this is at the origin.
But otherwise yes, if a terminal block is available for the DB that is a viable option.
[automerge]1587390970[/automerge]
4 X a/c units off one 30mA RCD no matter where you put it is bad design is likely to create nuisance tripping. individual RCBOs or MCBs are the way forward depending on your wiring from the board to the outdoor units.
As the garage is single phase then you need to clamp this phase at the 3 phase board and see what the load is one this phase first before banging 4 X a/c units in. You may need to jiggle a few single phase loads in the 3 phase board to get a best guess balance out of all three. They dont need to be perfect but you do need to do a max demand calc to ensure you are not hammering one phase.

Clamping the phase is no good, that only gives a momentary snapshot and not a picture of the overall loading.
A load study is the only sensible way to measure that.
 
Just to add a 100 amp switch or main RCD will not give you overload protection . An RCD is used to detected a fault current only and as others have said it's not a good idea to use an rcd to protect a distribution circuit.
 
The "least trouble" option is to feed the new DB from a 63A MCB in the existing board, and then put in separate MCB for each A/C unit, or RCBO if the A/C units have any need for additional protection (cable routes not guaranteed deeper than 50mm behind wall surface, etc). For the minimal extra cost I would go RCBO.

You won't get much selectivity between the A/C final breakers and the 63A feed, but making it 63A C-curve or D-curve would help, and also checking what the A/C specifications say they really need in order to select the smallest acceptable MCB/RCBO as well.
[automerge]1587380129[/automerge]
As already said, the A/C capacity is it heat-pumping ability and typically the input electrical power is less than half of that, but they do have motors starting and stopping so you might find the breaker specification is higher to allow for the surge.
[automerge]1587380353[/automerge]
Final thought, have to checked the feed arrangement to the garage DB you are planning on attaching to? You need to check the sub-main cable has both the necessary current carrying capacity AND low enough impedance to meet the voltage drop requirements.
[automerge]1587380462[/automerge]
A photo might help!

Reading the OP again it might be the mains supply enters at the garage, so no sub-main cable rating to worry about there, but the issue of looking at how the per-phase loads stack up still needs to be done.

the mains supply enters into the centre of the property and a sub main in the garage fed by a 25mm 3 core SWA. We were unable to enter the property due to the owners being out.
 

Attachments

  • 90878972-0966-4270-B5B6-699C62D5EAFC.jpeg
    90878972-0966-4270-B5B6-699C62D5EAFC.jpeg
    79.2 KB · Views: 33
the mains supply enters into the centre of the property and a sub main in the garage fed by a 25mm 3 core SWA. We were unable to enter the property due to the owners being out.

So you don't even know what size OCPD is protecting the submain?

I assume the galv adaptable box is being used as a spreader for the 25mm SWA? If so you could swap it for a larger box and put some of the bolted terminal type din rail terminals in there to split the feed to your new board.
 
So you don't even know what size OCPD is protecting the submain?

I assume the galv adaptable box is being used as a spreader for the 25mm SWA? If so you could swap it for a larger box and put some of the bolted terminal type din rail terminals in there to split the feed to your new board.

unfortunately not. I am going there on Monday (hopefully) and we will be able to get inside and look.

Yes it is and yes, that can be done. Is that essentially the same principle as a Henley block? Would I need a fused switch isolator before each board or is this just personal preference?

also, thank you everyone for your input, it’s been really interesting reading it all.
 
Yes it is and yes, that can be done. Is that essentially the same principle as a Henley block? Would I need a fused switch isolator before each board or is this just personal preference?

I guess you could say its the same principle, but I would say they are completely different things.
Any way you manage to hack Henley blocks into that installation is going to look like ,and likely be, a bodge

Why would you need a fused switch before each board? The question makes no sense to me, what is your logic behind suggesting this?
 
There is a spare 20A breaker on the non-RCD side that could be changed to something bigger to feed a 2nd adjacent DB, but the bigger question is the total load here, and also how it is distributed between the incoming phases.

As @davesparks said earlier, you need to do a load study (maybe helped by any documentation on the original design?) to see what loads are present and decide if it is reasonable to take it from here.

That should also re-visit this DB feed cable to see if it is OK for the increased load here with the A/C added. If 25mm SWA as you say it is almost certainly fine to the 100A load limit of that existing DB for current carrying but the volt drop might be too much. Again if the original calculations are available that might be simple, otherwise you need to determine the cable length in addition to establishing the new load/diversity, etc.

Splitting the SWA out to feed two boards might be tricky to do in any neat way, so unless you really need to, then taking it from a breaker in that board would be simplest. But only if all calculations work out, of course!
 
I guess you could say its the same principle, but I would say they are completely different things.
Any way you manage to hack Henley blocks into that installation is going to look like ,and likely be, a bodge

Why would you need a fused switch before each board? The question makes no sense to me, what is your logic behind suggesting this?

because I’m learning and just asking a question.
 
Looking at the potential load on the single phase board in the photo I think you need to check what else is fed of that phase from the three phase board. You may find that a new supply cable for the A/C of a different phase is a better idea.
 
Looking at the potential load on the single phase board in the photo I think you need to check what else is fed of that phase from the three phase board. You may find that a new supply cable for the A/C of a different phase is a better idea.

ok, I will have a look at what is on the other boards. Thank you.
 
because I’m learning and just asking a question.

It's a very specific question so you must have a reason for asking that question. So why do you think a fuse switch would be required?

It appears you aren't just learning but are attempting to complete work by getting the forum to do your designs for you.
 