Just to add a 100 amp switch or main RCD will not give you overload protection . An RCD is used to detected a fault current only and as others have said it's not a good idea to use an rcd to protect a distribution circuit.
 
The "least trouble" option is to feed the new DB from a 63A MCB in the existing board, and then put in separate MCB for each A/C unit, or RCBO if the A/C units have any need for additional protection (cable routes not guaranteed deeper than 50mm behind wall surface, etc). For the minimal extra cost I would go RCBO.

You won't get much selectivity between the A/C final breakers and the 63A feed, but making it 63A C-curve or D-curve would help, and also checking what the A/C specifications say they really need in order to select the smallest acceptable MCB/RCBO as well.
[automerge]1587380129[/automerge]
As already said, the A/C capacity is it heat-pumping ability and typically the input electrical power is less than half of that, but they do have motors starting and stopping so you might find the breaker specification is higher to allow for the surge.
[automerge]1587380353[/automerge]
Final thought, have to checked the feed arrangement to the garage DB you are planning on attaching to? You need to check the sub-main cable has both the necessary current carrying capacity AND low enough impedance to meet the voltage drop requirements.
[automerge]1587380462[/automerge]
A photo might help!

Reading the OP again it might be the mains supply enters at the garage, so no sub-main cable rating to worry about there, but the issue of looking at how the per-phase loads stack up still needs to be done.

the mains supply enters into the centre of the property and a sub main in the garage fed by a 25mm 3 core SWA. We were unable to enter the property due to the owners being out.
 

Attachments

  • 90878972-0966-4270-B5B6-699C62D5EAFC.jpeg
    79.2 KB · Views: 12
the mains supply enters into the centre of the property and a sub main in the garage fed by a 25mm 3 core SWA. We were unable to enter the property due to the owners being out.

So you don't even know what size OCPD is protecting the submain?

I assume the galv adaptable box is being used as a spreader for the 25mm SWA? If so you could swap it for a larger box and put some of the bolted terminal type din rail terminals in there to split the feed to your new board.
 
So you don't even know what size OCPD is protecting the submain?

I assume the galv adaptable box is being used as a spreader for the 25mm SWA? If so you could swap it for a larger box and put some of the bolted terminal type din rail terminals in there to split the feed to your new board.

unfortunately not. I am going there on Monday (hopefully) and we will be able to get inside and look.

Yes it is and yes, that can be done. Is that essentially the same principle as a Henley block? Would I need a fused switch isolator before each board or is this just personal preference?

also, thank you everyone for your input, it’s been really interesting reading it all.
 
Yes it is and yes, that can be done. Is that essentially the same principle as a Henley block? Would I need a fused switch isolator before each board or is this just personal preference?

I guess you could say its the same principle, but I would say they are completely different things.
Any way you manage to hack Henley blocks into that installation is going to look like ,and likely be, a bodge

Why would you need a fused switch before each board? The question makes no sense to me, what is your logic behind suggesting this?
 
There is a spare 20A breaker on the non-RCD side that could be changed to something bigger to feed a 2nd adjacent DB, but the bigger question is the total load here, and also how it is distributed between the incoming phases.

As @davesparks said earlier, you need to do a load study (maybe helped by any documentation on the original design?) to see what loads are present and decide if it is reasonable to take it from here.

That should also re-visit this DB feed cable to see if it is OK for the increased load here with the A/C added. If 25mm SWA as you say it is almost certainly fine to the 100A load limit of that existing DB for current carrying but the volt drop might be too much. Again if the original calculations are available that might be simple, otherwise you need to determine the cable length in addition to establishing the new load/diversity, etc.

Splitting the SWA out to feed two boards might be tricky to do in any neat way, so unless you really need to, then taking it from a breaker in that board would be simplest. But only if all calculations work out, of course!
 
I guess you could say its the same principle, but I would say they are completely different things.
Any way you manage to hack Henley blocks into that installation is going to look like ,and likely be, a bodge

Why would you need a fused switch before each board? The question makes no sense to me, what is your logic behind suggesting this?

because I’m learning and just asking a question.
 
Looking at the potential load on the single phase board in the photo I think you need to check what else is fed of that phase from the three phase board. You may find that a new supply cable for the A/C of a different phase is a better idea.
 
because I’m learning and just asking a question.

It's a very specific question so you must have a reason for asking that question. So why do you think a fuse switch would be required?

It appears you aren't just learning but are attempting to complete work by getting the forum to do your designs for you.
 
It's a very specific question so you must have a reason for asking that question. So why do you think a fuse switch would be required?

It appears you aren't just learning but are attempting to complete work by getting the forum to do your designs for you.

because before my DB at home I have a switch and I’m wondering if it is common practise or just someone has specified it.

I will be installing the cable to the aircon units but I will not be terminating it and this IS me just wanting to learn and work out for myself how it would be done, and funnily enough I was unsure so I came on to this forum for advice from lovely kind people such as yourself
 
because before my DB at home I have a switch and I’m wondering if it is common practise or just someone has specified it.

I will be installing the cable to the aircon units but I will not be terminating it and this IS me just wanting to learn and work out for myself how it would be done, and funnily enough I was unsure so I came on to this forum for advice from lovely kind people such as yourself

A switch, what type of switch and where is it installed? Is it a DNO provided isolator?

There's a big difference between a switch, a switchfuse and a fused switch.
 
A switch, what type of switch and where is it installed? Is it a DNO provided isolator?

There's a big difference between a switch, a switchfuse and a fused switch.

yes it is a DNO provides switch. I have my 100A fuse, the meter and then the switch. So I was wondering if this was common practise to have some form of switch to isolate the board or if this was just requested by previous owner.
 
yes it is a DNO provides switch. I have my 100A fuse, the meter and then the switch. So I was wondering if this was common practise to have some form of switch to isolate the board or if this was just requested by previous owner.

An isolator between the incoming supply and the consumers installation is an ideal scenario.
But that's very different to installing an isolator before every DB in an installation.
 

Reply to New Sub Board for aircon in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am installing a 14KW ducted aircon unit in a single phase house, which requires a 40A breaker. I was thinking of asking the electrician to put...
Replies
0
Views
413
I have a large gym in the garden and it gets ridiculously hot in the summer. I have utilised pretty much every inch of space and do not want to...
Replies
23
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
683
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock