The "least trouble" option is to feed the new DB from a 63A MCB in the existing board, and then put in separate MCB for each A/C unit, or RCBO if the A/C units have any need for additional protection (cable routes not guaranteed deeper than 50mm behind wall surface, etc). For the minimal extra cost I would go RCBO.
You won't get much selectivity between the A/C final breakers and the 63A feed, but making it 63A C-curve or D-curve would help, and also checking what the A/C specifications say they really need in order to select the smallest acceptable MCB/RCBO as well.
[automerge]1587380129[/automerge]
As already said, the A/C capacity is it heat-pumping ability and typically the input electrical power is less than half of that, but they do have motors starting and stopping so you might find the breaker specification is higher to allow for the surge.
[automerge]1587380353[/automerge]
Final thought, have to checked the feed arrangement to the garage DB you are planning on attaching to? You need to check the sub-main cable has both the necessary current carrying capacity AND low enough impedance to meet the voltage drop requirements.
[automerge]1587380462[/automerge]
A photo might help!
Reading the OP again it might be the mains supply enters at the garage, so no sub-main cable rating to worry about there, but the issue of looking at how the per-phase loads stack up still needs to be done.
the mains supply enters into the centre of the property and a sub main in the garage fed by a 25mm 3 core SWA. We were unable to enter the property due to the owners being out.
So you don't even know what size OCPD is protecting the submain?
I assume the galv adaptable box is being used as a spreader for the 25mm SWA? If so you could swap it for a larger box and put some of the bolted terminal type din rail terminals in there to split the feed to your new board.
Yes it is and yes, that can be done. Is that essentially the same principle as a Henley block? Would I need a fused switch isolator before each board or is this just personal preference?
I guess you could say its the same principle, but I would say they are completely different things.
Any way you manage to hack Henley blocks into that installation is going to look like ,and likely be, a bodge
Why would you need a fused switch before each board? The question makes no sense to me, what is your logic behind suggesting this?
Looking at the potential load on the single phase board in the photo I think you need to check what else is fed of that phase from the three phase board. You may find that a new supply cable for the A/C of a different phase is a better idea.
because I’m learning and just asking a question.
It's a very specific question so you must have a reason for asking that question. So why do you think a fuse switch would be required?
It appears you aren't just learning but are attempting to complete work by getting the forum to do your designs for you.
because before my DB at home I have a switch and I’m wondering if it is common practise or just someone has specified it.
I will be installing the cable to the aircon units but I will not be terminating it and this IS me just wanting to learn and work out for myself how it would be done, and funnily enough I was unsure so I came on to this forum for advice from lovely kind people such as yourself
A switch, what type of switch and where is it installed? Is it a DNO provided isolator?
There's a big difference between a switch, a switchfuse and a fused switch.
yes it is a DNO provides switch. I have my 100A fuse, the meter and then the switch. So I was wondering if this was common practise to have some form of switch to isolate the board or if this was just requested by previous owner.