Is there any other way to take this measurent apart from using a long lead????
 
Link at one end and test at the other:

Use calculation from

(r1+rn)/2
(r1+r2)-above=R2

thats the way I would do it. That's if you needed that figure alone.
 
Yes R1 + R2.

Switch off the breaker, connect line to earth on the circuit to test. Then at the accessory measure across line and earth (cpc) of the circuit, this way you confirm polarity as well as earth continuity, make sure you test at switches with them switched on. You then enter the result on your Schedule of tests in the R1+R2 box, and put a line through the R2 box. buy Guidance note 3, it explains everything you need to know about testing.

Cheers........Howard
 
Is there any other way to take this measurent apart from using a long lead????


Rip the cable out from it's installation and bring the furthest point back to the consumer unit.
 
for bonding conductors, you don'r have R1 or Rn. so that's out the window. long lead is only way. i just have a part coil of 6mm gn/y. and use that, then deduct the resistance of the lead ( i use a low ohms meter without a null facility.)
 
How else can it be done??
 
we all make mistakes, as the hedgehog said, climbing off the bog brush
 
  • Like
Reactions: 3 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
R2 measurement.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Thread Tags

Tags Tags
measurement

Advert

Thread statistics

Created
Electricalserv,
Last reply from
telectrix,
Replies
9
Views
6,939

Advert