P

Peter

Hello hoping someone can urgently help with an issue I am having.

I am carrying out electrical works on a 2 bedroom flat that is being refurbished. All I have done is changed single sockets to double sockets. Taken away a socket that was spured off another socket. Moved some lights into the middle of the ceiling and moved 2 light switches.

I am also not sure if the fault was already there or not but everytime I plugged in something that draws a fair amount of power I.e heater or grinder it would trip the rcd. I thought it may be an rcd fault so I moved the mcb to the other rcd and changed the rcd I thought was faulty. Now what is happening is when you plug something in that draws power it stays on but still trips the same rcd that I changed even though the mcb is not on that rcd side ?

What could this be ?
 
Likely to be a neutral-earth fault on a circuit on the side with the RCD that trips. Check the IR on all these circuits - it might have been pre-existing. The heavier the load, the more likely the trip, and it will happen regardless of which circuit the load is on.
 
You probably have an earth neutral fault, either existing or one you've created.....…...too slow.
 
Test first, not later then you can be sure if faults are existing.
 
  • Agree
Reactions: buzzlightyear
is the op a spark ? or some one pretending to be one .:rolleyes:
 
Any tests undertaken, other than the good old bang test?

Mind you, them were the days. None of this faffing around with meters and bits of paper.
 
But...

a) The problem was there before he changed anything in the board.
b) The circuit he moved now works, and doesn't trip its own RCD.
c) It trips mainly with heavy loads.

All three factors point at an N-E fault on any of the circuits on the RCD that trips, not necessarily the one that is loaded or the one he moved.

Sometimes I wonder if I'm the only person who actually reads the fault description before replying!
 
Do your testing first and find out exactly what it is changing rcds without finding the fault is false economy
 
Sometimes I wonder if I'm the only person who actually reads the fault description before replying!

I know, and do they read what other members have posted as well, present company accepted.
 
Hi - yep I'm going for the N-E fault too - and I raise that it's in one of the 1G to 2G outlet conversions you've just done (trapped N or some such) :) .
 
  • Like
Reactions: Midwest
Hello hoping someone can urgently help with an issue I am having.

I am carrying out electrical works on a 2 bedroom flat that is being refurbished. All I have done is changed single sockets to double sockets. Taken away a socket that was spured off another socket. Moved some lights into the middle of the ceiling and moved 2 light switches.

I am also not sure if the fault was already there or not but everytime I plugged in something that draws a fair amount of power I.e heater or grinder it would trip the rcd. I thought it may be an rcd fault so I moved the mcb to the other rcd and changed the rcd I thought was faulty. Now what is happening is when you plug something in that draws power it stays on but still trips the same rcd that I changed even though the mcb is not on that rcd side ?

What could this be ?
Did you move the neutral to the other neutral terminal block?
as this would be the reason that the other RCD could be tripping out
I think that the reason the RCD tripped out in the first place would probably due to a neutral to earth fault, if this is so you want to move circuit back (together with neutral) I can't see your profile so I hope that this is a DIY job and not a paid job if so there has been no mention of testing.
 
Hello hoping someone can urgently help with an issue I am having.

I am carrying out electrical works on a 2 bedroom flat that is being refurbished. All I have done is changed single sockets to double sockets. Taken away a socket that was spured off another socket. Moved some lights into the middle of the ceiling and moved 2 light switches.

I am also not sure if the fault was already there or not but everytime I plugged in something that draws a fair amount of power I.e heater or grinder it would trip the rcd. I thought it may be an rcd fault so I moved the mcb to the other rcd and changed the rcd I thought was faulty. Now what is happening is when you plug something in that draws power it stays on but still trips the same rcd that I changed even though the mcb is not on that rcd side ?

What could this be ?
Hello mate. Any idea as to the construction of this 2 bed flat? Would you know if the ceiling is suspended and fixed to tin hat?
 
If so I’d bet my bottom dollar that you’ve clipped a neutral when you moved the lights into the centre of the room which and the neutral is touching down on the tin hat
 
Do you ever assist anyone or say anything positive? I thought the whole point of this site was to help out fellow sparks
defiantly maybe.,
on this forum there will be a little criticism from time to time to people not knowing what their are doing .
has they say don't like the heat stay out of the kitchen (tin hat on )
plus flack jacket .
 
  • Funny
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD Keeps tripping and not mcb and not on the same side as MCB
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Peter,
Last reply from
Sparksaflyin,
Replies
24
Views
3,980

Advert