Not on any RCD I can recall. Test button connects a resistor between one pole on the input side and one of the other poles on the output side, creating a 30mA or so difference (on a 30mA RCD) between whatever current is flowing through those two poles.
No earth connection involved.
you may well be correct but I have known some rcbo's to not trip when the flylead is disconnected.
 
Possibly an extra test built in to ensure that the earth lead is connected, but not since the days of the old voltage operated earth leakage detectors (yes, I am that old), has there been a requirement for a current to flow in the cpc for said breaker to operate. RCDs detect a difference in the sum of the currents flowing through its poles. The sum should be zero, but if exceeds 30mA, then off it should trip.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Newcastle
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
RCD test button
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Lesly1,
Last reply from
brianmoooore,
Replies
7
Views
521

Advert

Back
Top