Afternoon all,

I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however, the wiring was old and did not have earths(they cut them off).

So I decided to completely rip out the old wiring including unnecessary spur and put brand new 2.5mm cable connected to 16A mcb.

However, it trips the RCD but not the MCB. I don’t understand why.

I replaced the McB with the spare one I had laying around, was doing the same thing. Removed the mcb opened it up saw burnt marks on the inside. Ok I thought it might the MCB, so I received a new one today, same thing.


Checked previously:

All the wiring to the socket is correct!
Continuity check all fine!
Checked for Earth leakage with multimeter seems to be fine.

What else could cause this ? 😔

P.S I’m not using it for anything heavy just a 2A NAS server.

Thanks
 
Usually wrong neutral bar , or wrong Wiring .does it trip before anything plugged in?
 
  • Like
Reactions: pc1966 and DPG
Have you carried out any IR tests?

You obviously have some sort of earth leak somewhere as this has only started happening since introducing the new cable with a cpc, as they cut it out of the old cable it wouldn’t have been possible to trip the RCD

Have you tried plugging something else into the socket? You might find that you have a fault appliance
 
Usually wrong neutral bar , or wrong Wiring .does it trip before anything plugged in?
No it doesn’t trip anything when nothing is plugged in. I also used the same cable and out it (just to test) on another 20A mcb and it worked fine.
 
No
No it doesn’t trip anything when nothing is plugged in. I also used the same cable and out it (just to test) on another 20A mcb and it worked fine.
You misunderstood what I said

Try and plug something else in. Grab your kettle or anything and plug it into this socket. If it doesn’t trip then whatever you are plugging into it is faulty.
 
No problem we have all done it !
 
  • Like
Reactions: timhoward

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD tripping when using loft socket.
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
archee,
Last reply from
Uplight99,
Replies
7
Views
1,897

Advert