hello everyone,
what code would you give if you see multiple usage of connector strips above the false ceiling?! ( to connect ceiling lights together,...etc without using any junction box)

Thanks
 
As Westy says… is it LV?

It could be 12V between downlights…. Where it needn’t be coded.
If it’s mains voltage, then agree C1…

I’d be checking cpc continuity while I’m there.
 
Even ELV should be contained and is a non compliance.
For protection against shock, at least, I thought that this wasn't always required, based on 414.4.5. Is there another reason that they might need enclosing, hidden away in the depths of the regs somewhere?

Basic protection is generally unnecessary in normal dry conditions for:
(i)SELV circuits where the nominal voltage does not exceed 25 V AC or 60 V DC
(ii)PELV circuits where the nominal voltage does not exceed 25 V AC or 60 V DC and exposed-conductive-
parts and/or the live parts are connected by a protective conductor to the main earthing terminal.
In all other cases, basic protection is not required if the nominal voltage of the SELV or PELV system does not
exceed 12 V AC or 30 V DC.
 
For protection against shock, at least, I thought that this wasn't always required, based on 414.4.5. Is there another reason that they might need enclosing, hidden away in the depths of the regs somewhere?

Basic protection is generally unnecessary in normal dry conditions for:
(i)SELV circuits where the nominal voltage does not exceed 25 V AC or 60 V DC
(ii)PELV circuits where the nominal voltage does not exceed 25 V AC or 60 V DC and exposed-conductive-
parts and/or the live parts are connected by a protective conductor to the main earthing terminal.
In all other cases, basic protection is not required if the nominal voltage of the SELV or PELV system does not
exceed 12 V AC or 30 V DC.
Fair point which goes against my thinking of Regulation 526.5
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dubai, UAE
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
All Other Countries (This Is English Speaking Website Only - WE don't mind Google Translate Users :)
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
recommended code for using connector strip
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Thread Tags

Tags Tags
using

Advert

Thread statistics

Created
arashabb,
Last reply from
arashabb,
Replies
10
Views
171

Advert

Back
Top