There not fused though are they?
https://www.-----------------------...et-outlets-incorporating-usb-charging-points/
That report covers many types of fault, not just over current protection.
There not fused though are they?
https://www.-----------------------...et-outlets-incorporating-usb-charging-points/
If you are talking about USB 13A sockets, since 2016 when the socket British Standard was revised to cover built-in electronics, the design has to incorporate a fusible link or fuse, and the psu must be SELV, meeting creepage and clearance distances and transformer insulation requirements etc. etc.Not going too off topic but technically now you mention it an unfused supply off a ring? maybe theres a reg being broken there.
I'd be interested to know if these sockets do have a fused link or fuse.If you are talking about USB 13A sockets, since 2016 when the socket British Standard was revised to cover built-in electronics, the design has to incorporate a fusible link or fuse, and the psu must be SELV, meeting creepage and clearance distances and transformer insulation requirements etc. etc.
USBs got off to a bad start before that revised standard, when the market was flooded with dubious products, though I think China also makes 'proper' ones now.
But these days I like to think if you buy an approved product from a reputable manufacturer/source, there should no longer be a problem!
Newer technology allows a phone or tablet you plug in to negotiate with the USB charger what voltage/ current it wants.
I guess you could say that's that's an added safety feature, or something else to go wrong!
But really I'm only referring to Rings etc Even if you took a selv spur of a Ring you have to fuse it.
You lost meNot going too off topic but technically now you mention it an unfused supply off a ring? maybe theres a reg being broken there.
hehe why notSELV spur? What on earth is that?

Well if the socket has a CB mark from an accredited test house, then it must have (eg. a fusible link - typically looks like a resistor!)I'd be interested to know if these sockets do have a fused link or fuse.
I can see the purpose of having a 1:1 transformer socket outlet.hehe why not![]()
I think he's on about a selv fan supply.SELV spur? What on earth is that?
I can see the purpose of having a 1:1 transformer socket outlet.
Only in specific cases where MCB and cable are specified together to meet adiabatic limit, etc.Fused plugs are only required in the UK where we use Rings.
the flex is protected by the Fuse/MCB at the DB on a radial.
I meant a BS 1363 type.For shaving?
Apparently there are people out there who shave.