No I mean theres two faults, malfunction transformer and broken leg.

One of the reasons we use fused plugs in the UK is because we use rings.

Ah I'm with you.

The USB sockets will have circuit protection built in if they are built to the appropriate standard.
 
it does seem a bit dodgy - the transformer malfunctions fine the MCB trips but on a ring there is also a broken leg and 32A MCB = fry time.

If the power supply for the USB outlets fails then the protection built in to that unit will operate.

A broken ring won't change how an MCB responds to a fault, it only affects overload situations.
 
Anything plugged into a Ring should be fused in case of a broken leg. With a broken leg it becomes a radial wired in 2.5 and a 32A MCB will not provide adequate protection.

No, see my previous comment. The socket will have built in protection, otherwise it would not meet the BS standards.

Edit, not sure I understand your point. I was answering your previous point about USB sockets not being fused.
 
"Previously, each mains socket had its own connection to the fuse board. To save copper, Britain adopted the ring main system, with sockets connected sequentially, but this meant each connection needed its own fuse. Instead of putting the fuses in the sockets, they were included in the plugs themselves."

Fused plugs are only required in the UK where we use Rings.

the flex is protected by the Fuse/MCB at the DB on a radial.
 
Not going too off topic but technically now you mention it an unfused supply off a ring? maybe theres a reg being broken there.
If you are talking about USB 13A sockets, since 2016 when the socket British Standard was revised to cover built-in electronics, the design has to incorporate a fusible link or fuse, and the psu must be SELV, meeting creepage and clearance distances and transformer insulation requirements etc. etc.
USBs got off to a bad start before that revised standard, when the market was flooded with dubious products, though I think China also makes 'proper' ones now.
But these days I like to think if you buy an approved product from a reputable manufacturer/source, there should no longer be a problem!
Newer technology allows a phone or tablet you plug in to negotiate with the USB charger what voltage/ current it wants.
I guess you could say that's that's an added safety feature, or something else to go wrong!
 
If you are talking about USB 13A sockets, since 2016 when the socket British Standard was revised to cover built-in electronics, the design has to incorporate a fusible link or fuse, and the psu must be SELV, meeting creepage and clearance distances and transformer insulation requirements etc. etc.
USBs got off to a bad start before that revised standard, when the market was flooded with dubious products, though I think China also makes 'proper' ones now.
But these days I like to think if you buy an approved product from a reputable manufacturer/source, there should no longer be a problem!
Newer technology allows a phone or tablet you plug in to negotiate with the USB charger what voltage/ current it wants.
I guess you could say that's that's an added safety feature, or something else to go wrong!
I'd be interested to know if these sockets do have a fused link or fuse.

But really I'm only referring to Rings etc Even if you took a selv spur of a Ring you have to fuse it.
 

Reply to Socket with slimest back connections? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
818
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
940
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB...
Replies
2
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock