No I mean theres two faults, malfunction transformer and broken leg.

One of the reasons we use fused plugs in the UK is because we use rings.
 
No I mean theres two faults, malfunction transformer and broken leg.

One of the reasons we use fused plugs in the UK is because we use rings.

Ah I'm with you.

The USB sockets will have circuit protection built in if they are built to the appropriate standard.
 
  • Like
Reactions: nicebutdim
it does seem a bit dodgy - the transformer malfunctions fine the MCB trips but on a ring there is also a broken leg and 32A MCB = fry time.

If the power supply for the USB outlets fails then the protection built in to that unit will operate.

A broken ring won't change how an MCB responds to a fault, it only affects overload situations.
 
  • Like
Reactions: nicebutdim
Possibly but on a ring it probably should be fused.
 
Possibly but on a ring it probably should be fused.

How do you know they aren't suitably protected? Have you opened them up to have a look?

These units are built to an appropriate product standard and designed specifically to be installed in UK installations.
 
  • Like
Reactions: nicebutdim
Anything plugged into a Ring should be fused in case of a broken leg. With a broken leg it becomes a radial wired in 2.5 and a 32A MCB will not provide adequate protection.
 
Anything plugged into a Ring should be fused in case of a broken leg. With a broken leg it becomes a radial wired in 2.5 and a 32A MCB will not provide adequate protection.

No, see my previous comment. The socket will have built in protection, otherwise it would not meet the BS standards.

Edit, not sure I understand your point. I was answering your previous point about USB sockets not being fused.
 
  • Like
Reactions: nicebutdim
Anything plugged into a Ring should be fused in case of a broken leg.

No, that's not why plugs have fuses in them.

The fuse in the plug is there to protect the flexible cable downstream of it.

The plug fuse does nothing to help in a broken ring circuit.
 
  • Like
Reactions: nicebutdim
There not fused though are they?

https://www.-----------------------...et-outlets-incorporating-usb-charging-points/
 
"Previously, each mains socket had its own connection to the fuse board. To save copper, Britain adopted the ring main system, with sockets connected sequentially, but this meant each connection needed its own fuse. Instead of putting the fuses in the sockets, they were included in the plugs themselves."

Fused plugs are only required in the UK where we use Rings.

the flex is protected by the Fuse/MCB at the DB on a radial.
 
There not fused though are they?

https://www.-----------------------...et-outlets-incorporating-usb-charging-points/

That report covers many types of fault, not just over current protection.
 
Not going too off topic but technically now you mention it an unfused supply off a ring? maybe theres a reg being broken there.
If you are talking about USB 13A sockets, since 2016 when the socket British Standard was revised to cover built-in electronics, the design has to incorporate a fusible link or fuse, and the psu must be SELV, meeting creepage and clearance distances and transformer insulation requirements etc. etc.
USBs got off to a bad start before that revised standard, when the market was flooded with dubious products, though I think China also makes 'proper' ones now.
But these days I like to think if you buy an approved product from a reputable manufacturer/source, there should no longer be a problem!
Newer technology allows a phone or tablet you plug in to negotiate with the USB charger what voltage/ current it wants.
I guess you could say that's that's an added safety feature, or something else to go wrong!
 
  • Like
Reactions: nicebutdim and DPG
If you are talking about USB 13A sockets, since 2016 when the socket British Standard was revised to cover built-in electronics, the design has to incorporate a fusible link or fuse, and the psu must be SELV, meeting creepage and clearance distances and transformer insulation requirements etc. etc.
USBs got off to a bad start before that revised standard, when the market was flooded with dubious products, though I think China also makes 'proper' ones now.
But these days I like to think if you buy an approved product from a reputable manufacturer/source, there should no longer be a problem!
Newer technology allows a phone or tablet you plug in to negotiate with the USB charger what voltage/ current it wants.
I guess you could say that's that's an added safety feature, or something else to go wrong!
I'd be interested to know if these sockets do have a fused link or fuse.

But really I'm only referring to Rings etc Even if you took a selv spur of a Ring you have to fuse it.
 
Just a thought, mk usb sockets advertise as fitting 25mm box, not sure about how well 3 cables would fit though.
 
I've seen a few I'm going to investigate. But I think Dave's post about the collar has cracked it.
 
Not going too off topic but technically now you mention it an unfused supply off a ring? maybe theres a reg being broken there.
You lost me
 
  • Like
Reactions: nicebutdim and DPG
I'd be interested to know if these sockets do have a fused link or fuse.
Well if the socket has a CB mark from an accredited test house, then it must have (eg. a fusible link - typically looks like a resistor!)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Reading
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Socket with slimest back connections?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
48

Advert

Thread statistics

Created
Mark Wright,
Last reply from
Mike Johnson,
Replies
48
Views
5,439

Advert