As its a socket should be on a RCD anyway, in which case Zs up to 1667ohms.

Not Correct!

RCD is backup / supplementary protection to the main protection.

Will the RCd trip the circuit? when there is a shortcircuit? and the cable burns the house down?
because the CB did not trip, because the Zs was too high?:laugh3:
 
Last edited by a moderator:
This log cabin, does it have it's own metered supply? Or, is it fed by a distribution circuit from another building?

If the latter, then what is this Ze you quote? Ze at the supply or at the cabin board (ie Zdb)?

Looks to me like we're missing some info.

Anyway up, those Zs figures (assuming that's what they are, you don't state explicitly) are somewhat astray. Poor or varying Zs at sockets can be due to bad connections at the pins or dirt/corrosion on the switch contacts. Have you tried flicking the switches a few times to 'clear' the contacts?
 
Not Correct!

RCD is backup / supplementary protection to the main protection.

Will the RCd trip the circuit? when there is a shortcircuit? and the cable burns the house down?
because the CB did not trip, because the Zs was too high?:laugh3:

I'm not disagreeing with the need to try and find out why the Zs is high but:

411.4.4 - An RCD can be used for fault protection with an overcurrent protective device also in place.

When does anybody measure the Z between neutral and line to ensure that an MCB will trip? The only measurement you make is Isc at the origin!
 
Not Correct!

RCD is backup / supplementary protection to the main protection.

Will the RCd trip the circuit? when there is a shortcircuit? and the cable burns the house down?
because the CB did not trip, because the Zs was too high?:laugh3:
your not measuring line voltage or short circuit with a Zs Moses.....
 

Reply to Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
Replies
24
Views
5K
carried out dead testing on new site accommodation,all dead tests were fine however, when I conducted live testing I got high zs redings on...
Replies
16
Views
3K
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and...
Replies
53
Views
5K
This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do...
Replies
30
Views
10K
Hi, I was wondering if you guys can help with some errant test results. I'm testing a ring and i get L-L = 0.41 N-N = 0.40 E-E = 0.63 Great...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock