I'm not disagreeing with the need to try and find out why the Zs is high but:
411.4.4 - An RCD can be used for fault protection with an overcurrent protective device also in place.
When does anybody measure the Z between neutral and line to ensure that an MCB will trip? The only measurement you make is Isc at the origin!
Zs is always measured between CPC and L conductors.
This is because, in UK we use a reduced size CPC, so if the Zs is ok when measured with CPC-L fo a fault current, then its obviously OK between L-N for a short circuit current!!!
its always measured between CPC and L conductors because thats what Zs is....earth-fault-loop-impedence.....nothing to do with short circuit...
your not measuring line voltage or short circuit with a Zs Moses.....
Where have you bin man?
Zs is measured at the furthest point in the circuit and not at the CU, as some have suggested. Ze is measured at the CU.
Zs is measure of how much short circuit current will flow, when any circuit is short circuited at its furthest, and that this short circuit current will trip the CPD in the requisite time(0.4/5.0 sec)
According to your readings that circuit warrants further investigation.
Wip the sockets off there is only 6!
your ring final doesnt really add up.
your Zs readings are way out.
where did you perform your ring final? - at the board or at a socket?
If you do ever do it at a socket make sure you disconnect earths from earth bar and put in a chock block same goes for neutrals
this prevents any parallel paths.
For simpletons, yes you r r8
But before the RCDs
CB's used to protect us against earth faults and short circuit faults. They did then and they do now even without the RCD's.
RCD's are there because of their sensitivity and speed.
As I said before, Zs is measured between L-E
1.because CPC is a smaller size conductor, i.e. R2 is larger than Rn, i.e. Zs measured with R2 is a higher value than measured with Rn, giving you the worst case Zs.
2.because it ensures the continuity of CPC.
You'd better understand more clearly what Zs is!
Zs is measured between Line and earth, so if a fault to earth happens it ensures enough current will flow through the fault to trip an MCB.
For a short circuit to trip a MCB there needs to be an overload or L-N fault but the impedance to ensure the MCB trip in overload is never measured!
Zs is a measure of the earth fault loop impedance path, not short circuit impedance (L/N)
A measure of how much short circuit current will flow, when any circuit is short circuited (perhaps at its furthest point) is PSCC
But before the RCDs
well firstly in answer to your question where have i been....well...over st helens way today Moses......and simpleton?...i think youv got me confused with someone else fella....oh, by the way....when did i mention Ze? another thing n all.....you refer to the CPC being a smaller CSA than live conductors...is this always true Moses?...what about metal conduit with 2.5mm CSA single live conductors......
AQUOTE=yellowvanman;533036]You'd better understand more clearly what Zs is!
For a short circuit to trip a MCB there needs to be an overload or L-N fault but the impedance to ensure the MCB trip in overload is never measured![/QUOTE]
Vanman my friend
I think you must agree, that if 6A a breaker will trip with a 7A fault current(CPC-L), then it surely will trip with a 8A current short circuit(L-N).
As Zs between L-E has a higher value, than Zs between L-N, only Zs for L-E is measured.
CPC wire on a 6mm T&E is 2.5mm, and N wire is 6mm.
Therefore current through the L-CPC path( 6mm+2.5mm) will be less, than the Current through L-N path(6mm+6mm).
If there is no earth continuity then its potentially fatal, but if Neutral is missing or non continuous then it no big deal, it comes apparent in the functional test.
Reply to Socket Zs High in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N...
5K
carried out dead testing on new site accommodation,all dead tests were fine however, when I conducted live testing I got high zs redings on...
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and...
5K
This has messed my head up so much I’m not sure I can even explain it properly but hopefully someone out there may give me ideas of what to do...
10K
Hi, I was wondering if you guys can help with some errant test results. I'm testing a ring and i get L-L = 0.41 N-N = 0.40 E-E = 0.63 Great...
4K