rallyandy

I went to look at a hotel today, the first thing is the old boards which have various gaps and 3Ka breakers JB's everywhere, and look at the recorded results !!IMAG0304.jpgIMAG0305.jpgIMAG0306.jpg
 
Looks like only the Zs for the socket circuits were actually tested, the rest calculated.
 
thats what i thought as well, look at the second socket circuit the Zs reading is higher than the R1 + R2 reading
 
how doi enlarge the pic big enough to read it? i can just read "circuit details" , but none of the entries.
 
Left click on the image, then you should get a magnifying glass with a + in it.
Remember to back page, rather than close the window, otherwise you'll close the browser.
 
Left click on the image, then you should get a magnifying glass with a + in it.
Remember to back page, rather than close the window, otherwise you'll close the browser.

thanks for that. it works. remember not to employ me for anything to do with computers, esp. software. LOL.
 
I have seen this quite a lot. They used to say that you were not allowed to do a ZS reading at any point other than a socket due to the exposure of live parts (with a socket you can use a plug top tester) so the only way to get a Zs was (R1+R2)+Ze, the R1+R2 that is lower than the Zs is most likely due to a parallel earth path (eg bonding) and as this was the only real test, shows in the results. Not sure what the norm is in regards to Zs testing now, I just throw the covers off and get in their with my tester.
 
I have seen this quite a lot. They used to say that you were not allowed to do a ZS reading at any point other than a socket due to the exposure of live parts (with a socket you can use a plug top tester) so the only way to get a Zs was (R1+R2)+Ze, the R1+R2 that is lower than the Zs is most likely due to a parallel earth path (eg bonding) and as this was the only real test, shows in the results. Not sure what the norm is in regards to Zs testing now, I just throw the covers off and get in their with my tester.

i was thinking on the lines that they would have stayed with one method of testing the circuitsi, ie all the rooms have one 2.5 T&E radial for one socket and one 1.0 T&E for lighting, so surely if the Ze is recorded as 0.09 then for instance if you add the R1 + R2 of 0.71 the Zs should be 0.8 ? or is it me being a bit dumb lol
 
by calculation, you are correct, but due to parallel paths (water pipes etc.) to earth, the Zs can be lower than calculated. this is most noticeable in TT systems where the resistance to earth through services is less than the resistance through the earth rod.
 
  • Like
Reactions: 1 person
by calculation, you are correct, but due to parallel paths (water pipes etc.) to earth, the Zs can be lower than calculated. this is most noticeable in TT systems where the resistance to earth through services is less than the resistance through the earth rod.

it just didn't look right to me, this is just one sheet of many for the various boards around the Hotel and they all vary, i just thought the results would be similar on the other boards and circuits if there were parallel earth paths, plus i looked for supplementary bonding but couldn,t find any only main bonding so far, ( I must be on a bad day lol) and its TNS
 
by calculation, you are correct, but due to parallel paths (water pipes etc.) to earth, the Zs can be lower than calculated. this is most noticeable in TT systems where the resistance to earth through services is less than the resistance through the earth rod.

This is why the Zs-Ze = (R1+R2) formula should never be used as it makes no allowance for the parallel paths that exist in all but the most basic of 'all-insulated' installations.
 
  • Like
Reactions: 1 person
take a few readings and compare with them. that should give an idea.
 
  • Like
Reactions: 1 person
i,m back ther tomorrow so will start taking my own readings, i was going off the existing readings today for an overview of the existing installation
 
i think i need to review my test procedures , i have always measured Ze at the supply incomer, then R1 + R2 and added them together obviously not allowing for parallel earths, you learn something new every day on here and i dont mind admitting it
 
i always measure Zs unless by doing so i might create danger for myself or others. to give an idea of the effect of parallel paths, measure Ze as normal with the main earth dissed. then measure again with it connected. you should find the 2nd reading is lower.
 
i think i need to review my test procedures , i have always measured Ze at the supply incomer, then R1 + R2 and added them together obviously not allowing for parallel earths, you learn something new every day on here and i dont mind admitting it

Your procedure still complies, measurement or calculation.

I'm a confirmed measurer!
 
  • Like
Reactions: 2 people
i always measure Zs unless by doing so i might create danger for myself or others. to give an idea of the effect of parallel paths, measure Ze as normal with the main earth dissed. then measure again with it connected. you should find the 2nd reading is lower.

I will try that tomorrow as the hotel is vacant week days and see what results i get , many thanks Telectrix
 
Hi guys ... just to keep you updated ... i havent been back to the job yet but should be back there monday so will let you know what i find
Andy
 
to give an idea of the effect of parallel paths, measure Ze as normal with the main earth dissed. then measure again with it connected. you should find the 2nd reading is lower.

Shouldn't this be done anyway, as your as part of your PFC test (PEFC) ?
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Spot the mistakes - Billy Bulls**t circuit sheets i think
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
rallyandy,
Last reply from
spark 68,
Replies
24
Views
3,331

Advert