i think i need to review my test procedures , i have always measured Ze at the supply incomer, then R1 + R2 and added them together obviously not allowing for parallel earths, you learn something new every day on here and i dont mind admitting it

Your procedure still complies, measurement or calculation.

I'm a confirmed measurer!
 
  • Like
Reactions: 2 people
i always measure Zs unless by doing so i might create danger for myself or others. to give an idea of the effect of parallel paths, measure Ze as normal with the main earth dissed. then measure again with it connected. you should find the 2nd reading is lower.

I will try that tomorrow as the hotel is vacant week days and see what results i get , many thanks Telectrix
 
Hi guys ... just to keep you updated ... i havent been back to the job yet but should be back there monday so will let you know what i find
Andy
 
to give an idea of the effect of parallel paths, measure Ze as normal with the main earth dissed. then measure again with it connected. you should find the 2nd reading is lower.

Shouldn't this be done anyway, as your as part of your PFC test (PEFC) ?
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Spot the mistakes - Billy Bulls**t circuit sheets i think
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
rallyandy,
Last reply from
spark 68,
Replies
24
Views
3,331

Advert