couple of questions on these, we just had a client drop these on me to install. Just reading the tech on them, im a bit unsure of the master slave scenario on them.
So far i see the master can have 2 strings fitted, to a max input voltage of 410 v DC. Now we have an array of 16 panels, so obviously i have split these into 2 x 8 panel strings. My thinking 410v per input.Or is it 410v for both combined.
My question is do i have to put one string in the master and other in the slave. Or do as i suspect use both on the master, and keep the slave disconnected.
Any help on this would be appreciated. Just not clear cut in my head. lol
stc below
235w panels x16
Voc 37.0V
rated voltage 29.5V
Isc 8.54A
rated current 7.97A
Regards
Steve