Hi People

So im testing my ring rinal circuit....

i do my end to end test.....

I join incoming CPC to outgoing Line and vice versa......

I then go around my circuit with my tester noting the readings at each socket and record the highest reading.....


Ok so this is my R1+R2 = 0.3

My measured Ze is 0.17Ohms

So my Zs = 0.29 + 0.17

Zs calculated is = 0.46....


Ok so now i reconnect the line and earth in the terminals and liven up my circuit (I have already done the insulation resistance also sorry didnt mention)

Then i goto the socket i got the highest R1+R2 at and do my Zs....


I get a result of 0.31Ohms

Can anyone explain how this is possible?

If Zs= Ze + (R1+R2)

How can i get such different results between calculated and measured?????


Spoke to my friend who has been around a long time and he tells me he does his R1+R2 at the consumer unit.... even though in the OSG it says the way i did it was correct.

When i do it his way i get slightly different readings but they still do not work out in the end....

The circuit is otherwise sound.

Im really looking forward to the replies, oh and yes the leads were nulled


Darren
 
parallel paths reduce the measured Zs. so your readings seem fine to me.
 
think that was his R1+R2 and on the line above he'd rounded it up. to 0.30
 
Im with you on this..... if i disconnect the main bonding and retest? theres nothing plugged in within the circuit either
 
although threres no supplimentry bonding either in this circuit im wondering where the parallel path could be
 
Im with you on this..... if i disconnect the main bonding and retest? theres nothing plugged in within the circuit either

What are you trying to achieve though, parallel paths are fine!

Even in a simple 'insulated' domestic installation, you have parallel paths everywhere from protective bonding to boiler connections etc. etc.
 
Last edited:
Im simply testing the equation Zs = Ze + (R1+R2)

and understanding why i can get different measured results to calculated

I do understand the drill just this was niggling me a bit
 
Im with you on this..... if i disconnect the main bonding and retest? theres nothing plugged in within the circuit either

Hope you don't mean Zs testing after removing a protective conductor. This should never be done.

Measured Zs is always expected to be lower than Ze + R1 + R2 due to the parallel paths connected to the MET whilst Zs testing.
 
I said bonding not main protective Conductor

thanks for the input like i said i just wanted to get the result as calculated. as a lot of sparks will calculate and be happy with the result
 
basically the answer is parallel paths....

The fact that the Zs is lower than Ze + (R1+R2) is fine on the test certificate.

Thanks everyone much appreciated!
 
basically the answer is parallel paths....

The fact that the Zs is lower than Ze + (R1+R2) is fine on the test certificate.

Thanks everyone much appreciated!

That's about it, a competent person reading the test results would expect that scenario.
 
That's about it, a competent person reading the test results would expect that scenario.

Correct, and in actual fact if the Measured Zs recorded on the SOTR was equal to the recorded Ze plus the recorded R1 + R2 then a competent person checking your results would be very suspicious of your R1 + R2 readings. He would probably suspect that they weren't resistance readings at all. ;0)
 
Correct, and in actual fact if the Measured Zs recorded on the SOTR was equal to the recorded Ze plus the recorded R1 + R2 then a competent person checking your results would be very suspicious of your R1 + R2 readings. He would probably suspect that they weren't resistance readings at all. ;0)

Lol, but do remember that in accordance with Guidance Note 3, calculation of Zs from Ze+(R1+R2) is acceptable
 
So to eliminate parallel paths a calculations probably better, or do both and if he measured result is less than the calculated it can be down to parallel paths whith is acceptable

All good stuff guys!

Be reading GN3 again!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Testing Ring final circuits
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
Bonse,
Last reply from
Bonse,
Replies
26
Views
8,277

Advert