However, there is no mention of an EIC issued after a consumer [unit] changeover being acceptable! Do the same conditions apply in England and Wales?
Because it isn't acceptable - it would only certify the replacement of the distribution board and not the rest of the electrical installation.
Then a fuseboard would be a minor works. Not a EIC which it cant be. Your changing the makeup of the installation by fitting a new board. So should be tested fully. Otherwise you would have departures as long as your arm, either way the contractor would still be at fault.
Reactions: Billsays
How would you? Your certificate in no way relates to the existing wiring.
I don't think both of you guys haven't made your points clear?
  • Funny
Reactions: Billsays
I agree with b, if you change the ccu you should do a full test on the installation. If the installation fails in any way there would be a record in the "Schedule of items tested" and "comments on existing installation" using additional pages if necessary. The EIC should be sufficient.
And i know a lot of the sole traders on here frown upon the NIC etc but at least we get one inspection more than you guys a year!;)
Reactions: b-spark
You verify that the wiring won't adversely affect the safety of your DB installation, and that your DB installation won't adversely affect the safety of the existing wiring. You do not, however, take ownership of the existing wiring and the Electrical Installation Certificate in no way certifies the existing wiring.
Not sure what sole trader has to do with it. I have an annual assessment by the NICEIC and an annual inspection & audit by RECI so I'm certainly not afraid of having my work scrutinised.
I agree
Where has this idea that changing a consumer unit involves testing the whole installation?
Where has this idea that having tested for safe connection of the circuits to the new consumer unit,it can somehow be a replacement for a Eicr ?
The Eic is for the work involved with the consumer unit only,the Eic will reference that particular job,in my opinion it has nothing whatsoever to do with condition reporting and the testing and inspection that a Eicr requires
Reactions: Risteard
On point one, if you do a test then surely you have "taken ownership" (hate that expression btw) of the installation, last person working on it and testing it etc.
On your 2nd I think your on the same page as me. Our assessor comes around once a year but it's probably once a year more than the sparks on here who snipe at the schemes.
I snipe at the schemes and they thoroughly deserve a sniping :)
In the last 10 or so years they have been nothing less than a complete and utter embarrassment to what was the respected trade of electrician
I say that as someone who has worked under their umbrella for most of my working life
Your probably right Des, they are a racket!:D
But on your other post about "Where has this idea that changing a consumer unit involves testing the whole installation?"............
Once you have disconnected the final circuits from the supply, you have to ensure they are safe before re-energising them. You can only do that if you know ADS will work, the insulation is up to scratch and there are no mechanical defects likely to give rise to danger. So you're stuck with having to do a full test and all that entails, or you would be working outside the scope of BS7671.
Also remember you will have altered the breaking current of the protective devices if you've swapped out from a fuse board to MCBs, so they'll be carrying more fault current for a shorter time. Whether the existing circuits are up to this can only be determined by testing them.
How will the prospective fault current on these circuits have changed?
Reactions: Billsays
Yes sorry i worded that wrong and can't edit it, the PFC doesn't change (but the new device can carry a lot more fault current)
Landlord - Electrical Safety Certificate
David Steel,
Billsays,