Hi,

I am training to become and electrician, I have passed my C&G level 2 exams. I am working as an electrical improver.



I came across a consumer unit today, which has two main switches and two phases L2 and L3 supplying it.



Does this board comply with regs?



Can you take 2 phases to a consumer unit?

31649325_1836209529831911_725720731379302400_n.jpg
 
Is it rated for 400V and 25kA?
 
  • Agree
Reactions: 1 person
Is it rated for 400V and 25kA?

It is just a consumer unit. A metal box cant be rated for 400v.
The switches are rated correctly for the voltage and current they are being used for.
There is a 400v warning sticker on it.
 
The cable dressing police will be along in a moment to comment on the untidy cables....
 
  • Funny
Reactions: JK-Electrical
It is just a consumer unit. A metal box cant be rated for 400v.
An enclosure and assembly absolutely can be rated for 400V or not as the case may be.
 
Ok well I am thinking why are there three neutrals on the first block on the right does this mean the neutral will be switched off with the first main switch, it is a bit hard to follow where the three neutrals go.
 
Also I notice that 6kA rated devices have been used.
 
  • Like
Reactions: Vortigern
that is not what I call coacher ,wrong board their boy .
 
Dual tariff board?
 
T
An enclosure and assembly absolutely can be rated for 400V or not as the case may be.

There is nothing on the metal box which identifies it as being rated for anything, The switches are rated for 400v. But they are only subject to 230v each?
It is a normal domestic consumer unit?

switch.jpg
 
T
An enclosure and assembly absolutely can be rated for 400V or not as the case may be.

There is nothing on the metal box which identifies it as being rated for anything, The switches are rated for 400v. But they are only subject to 230v each?
It is a normal domestic consumer unit?
 
Ok well I am thinking why are there three neutrals on the first block on the right does this mean the neutral will be switched off with the first main switch, it is a bit hard to follow where the three neutrals go.
Incoming neutral goes to 1st neutral bar.
Then linked from there to each switch
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Can you take 2 phases to a consumer unit?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
135

Advert

Thread statistics

Created
Gigsy,
Last reply from
Bobster,
Replies
135
Views
17,718

Advert