We have been asked to do some redial work picked up by a testing company i a hostel. It has been picked up that is no RCD protection in the rooms

There are 5 submain circuits that feed the 20 consumer units, 4 consumers units per submain (B32) Each room have a consumer unit which has two double sockets off a 16a radial and a lighting.

They asked my advice on whether to change the submain MCB to RCBOs or whether to change the consumer units for main switch and RCBOs

They supply cables to each consumer unit are above a plasterboard ceiling but cant be sure of the installation method, does the submain need to be RCD protected? As i dont want to put RCBOs on each circuit and also on the submain also

Thanks
 
If the installation method of the sub-main requires RCD protection then how will fitting RCBOs on the final circuits protect the sub-mains?

That's my question, do the submains need to be RCD protected? Seems ridiculous that i need to install an RCD on the submain when it protects 4 consumer unit. It would be much better to be able to install separate RCBOs on the consumer unit and leave the submain.

Does above plasterboard ceiling count as buried? Or require an RCD
 
Whilst cables above ceilings and below floors require additional protection where they pass through joists or battens. RCD protection is not an acceptable method.
 
Does above plasterboard ceiling count as buried? Or require an RCD

If you screwed a 50mm screw into the ceiling would it hit the Submain anywhere along it's length?
 
Whilst cables above ceilings and below floors require additional protection where they pass through joists or battens. RCD protection is not an acceptable method.

How would you get over my issue?
 
What type of cable are the subs and what edition of the regs was the original work done to?
 
Seems to me, that you have been asked to supply RCD protection for the rooms.
I’m assuming that’s for socket-outlets and circuits of locations containing baths or showers?
You can either install an up front RCD for each room, or swap MCBs for RCBOs.
How you do that is up to you.
 
What type of cable are the subs and what edition of the regs was the original work done to?

Im not sure on the depth and the cable is T&E
 
I have just re-read the op.

The EICR that was done has highlighted a lack of RCD protection on final circuits on all CUs.

The client is trying to cut costs by asking if fitting ‘up front’ RCDs on the sub-mains instead of the CUs therfore installing five RCBOs rather than 40.

This is not an option due to selectivity so I would say no to that.
 
Im not sure on the depth and the cable is T&E
If the cables are just laid on plasterboard, there’s no requirement for a minimum depth.
The drill through the plasterboard, the drill will push the cable away.
Where cables run through joists or battens, the drill can’t push the cable away, so additional protection is required.
1.Depth between cable and the surface of the floor or ceiling has to be greater than 50mm.
2.Earthed sheath, conduit or trunking.
3.Steel plate between the ceiling/floor and the joist/batten.
Unlike for cables concealed in walls, RCD protection is not an option.
 
My take on this is that if it was installed to the 16th edition or before then the sockets don’t require the additional protection unless they could be reasonably expected to be used for outdoor equipment.
 
  • Disagree
Reactions: 1 person
My take on this is that if it was installed to the 16th edition or before then the sockets don’t require the additional protection unless they could be reasonably expected to be used for outdoor equipment.
Yes, that’s correct.
Only started needing RCD protection when the 17th came in, as they would be used by unsupervised ordinary persons.
 
  • Agree
Reactions: 1 person
The thing is we don’t know when it was installed. We also don’t know if the guy who issued the report is aware of the changes between the 16th and 17th. My point is that I’d like to know these facts before banging in RCD’s.
 
The thing is we don’t know when it was installed. We also don’t know if the guy who issued the report is aware of the changes between the 16th and 17th. My point is that I’d like to know these facts before banging in RCD’s.
Personally, If I’m asked to provide RCD protection, the age of the installation doesn’t matter.
I’ve done some work for a customer who owns a Cafe.
Installed a split load board a few years back, installed a new circuit for his dishwasher, installed some 600mm X 600mm LED lights, and a few other things.
Not all at the same time, but over a period of years.
The latest was to swap out the innards of the split load board and replace with RCBOs.
 
  • Like
Reactions: DPG
The client may well have done a risk assessment and the remediation is the provision of RCDs given it is a hostel, so surely the basis upon which it was wired is hardly relevant ?

The correct solution would be an RCD for each room for obvious reasons and is surely the right answer ?
 
The client may well have done a risk assessment and the remediation is the provision of RCDs given it is a hostel, so surely the basis upon which it was wired is hardly relevant ?

The correct solution would be an RCD for each room for obvious reasons and is surely the right answer ?
We don’t know that bud but it is possible. It’s also possible that the person that carried out the report wasn’t aware of the requirements of additional protection in the previous editions of the regs. Anyway we can speculate all night as I doubt we’ll ever know the full facts.
 
When I do EICRs I am not overly interested when it was installed with regard to additional protection it is a statement of fact it is not provided.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
RCD Protection for submains
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
96

Advert

Thread statistics

Created
TJC1,
Last reply from
Ian1981,
Replies
96
Views
36,201

Advert