Looking at the data sheet, and applying the UK regulation's approach but with USA value, it would be:
- Max current for 0.4s trip time = 30 * In (slightly less, but that is marked on horizontal scale) so that = 30 * 15A = 450A
- Assuming you are looking at the USA supply of 277V nominal line-phase and that is +/-10% then the lowest supply is 277 * 0.9 = 249V
- So max Zs = 249V / 450A = 0.55 ohms
- As for the table I did earlier, I am not applying the typical 0.8 factor for hot cable resistance compared to cold design/test values.
That is about 4 times lower than the European style of B-curve MCB would require, and that puts you cable size up massively! Assuming copper and matching CPC, that is no more than 0.27 ohms per conductor, and over 1280m that is 0.215 mOhm/m so you are looking at 3/0 AWG!
Realistically if you are faced with that sort of a breaker curve I would be looking at putting in a high quality RCD of 300mA or even up to 5A trip point as it would deliver far faster disconnection in the event of an earth fault, not having inrush trip risk, and allowing a sane cable size based on 5% VD of something like #5 AWG copper.