It is good news that you have an all RCBO board, that should help the electrician narrow down the fault.
Circuits 4 and 12 both labelled 'Kitchen Sockets' on 16A MCB's so does look like the circuit has been split with the fault on circuit 12 side.
Reactions: DPG and James
Yes but I intentially tripped no4 and it didn’t kill any kitchen sockets?
Yes to the kitchen sockets. No further as of yet.
You know any decent fault Finding electricians in Cambridgeshire area 😂
  • Optimistic
Reactions: James
Never know, if you let Artisan electrics do it on YT you might get it for free :tearsofjoy:
Edit: It should be getting a fair bit simpler to solve at this point though, limited to a number of sockets, and therefore cables.
We did initially think of them for our EICR but they were EXPENSIVE!
Always tempted by a freebie but not sure about my house featuring on YT if I’m honest.
Reactions: DPG and Bluetit
So the whole kitchen (sockets) is on a 16A radial circuit?
Can you tell if the cables and pipework come into contact with one another at some point?
Hot water is just pressurised or gravity? No pump or heater involved?
Perhaps unplug every appliance on that circuit and see if it still trips but I'm sure the other sparks have tried that.
Being an intermittent fault it will be or can be difficult to locate.
What insulation resistance does the certificate show for that circuit(12)
It was only put in yesterday. Not when they installed the board.
I believe yes. I think they downgraded it from 32amp?
The hot water is from a combi boiler.
Can’t see any issues to the eye with wires etc.
The electrician needs to come in the evening when you are able to recreate the fault. Assuming it is consistent in the evenings with the kitchen hot water on. It should be fairly easy to narrow down the item/leg of the radial causing the issue with an mft if the fault remains for 20mins or so at a time.
What was only just been put in, the mcb if not the board? When was the new board installed? and you dont have a test certificate yet?
Seems naive of you and the electrician to think a new board would solve the tripping fault.
Being on a separate RCBO will help minimise the inconvenience though and help locate it but you had already established it was the kitchen socket circuit.?
The RCB was only just put in.
The board was last week and yes we have the cert already.
The new board was not only because of the tripping but because the other was very old.
We couldn’t narrow it down before as it tripped the whole bank.
JP0704
Saffron Walden
Potential boiler issue
JP0704,
JP0704,