What you are looking for is the 14th edition reg Electrically & Mechanically Sound if you get a good Zs then your good to go thats why sparks put an earth tail between the socket and the backbox as when you unscrewed the socket you would have lost the earth. Nothing wrong with conduit as an earth .
Guys, thanks for some of your replies. My question is.. If there is no earth on the ring main and it turns out not to be in earthed conduit which I don't think it is, do I recommend a rewire or is there any other option? And as far as diving in first without testing that's not the case. I think you find we inspect first then test which is exactly what I'm doing. The first fix in the bathroom is being installed and is dead until connected up which will be tested first of course. As far as class 2 sockets you know what I meant plastic not metal. And I connected the cpc from the spur to the earth terminal but like I said it doesn't look like an earth is going back so makes no difference at the moment. Pleas guys if your not going to reply with any helpful answers don't bother. Thank you.
Do your testing tomorrow and you may find that the conduit is a very good earth path
If you are trying to make the sockets safer when they are removed whilst live,you would be better off fitting tail earths to the back boxes (if there are none )
If the conduit is not intact,it may still be possible to wire a seperate earth through the system,but probably easier to rewire all in singles through the conduit where it is still possible to do so
Oh and the reason I discovered there is no earth in the ring main is because I intend to run a 13 amp fuss spur for the underfloor heating for the bathroom off the ring main so I had to take a look at the socket on the landing which turned out to be in a bit of a state. I can run a radial from a spare mcb to power the stuff in the bathroom if I have to and I can ensure my work is earthed and safe but I am simply trying to find out what advise you guys would give about the lack of earth in the ring main as I don't want be accused of scare mongering by suggesting a rewire if there is another solution.
Thanks Des yeah I'm hoping there is conduit like with the lighting circuits, fingers crossed. So basically If there is earthed conduit I'm all good, if there is conduit but no continuity I can try to earth it myself somehow if not its suggest a rewire time. That's all wanted to confirm, thanks mate.
I would do the job I was contracted to carry out
I would advise the customer of the percieved problem
I would suggest a solution if they asked of me
I would not make a suggestion unless asked (that would put aside your scaremongering concern )
There is nothing wrong with making danger known to the customer
Other things spring to mind as you are clearly doing this work for a client.
Bonding....circuit protection....certification/notification,it comes under part p.
Well you will be scaremongering remember you cannot backdate the regs when these sockets were installed they complied to to the then regulations so if they pass IR Zs tests its good to go as for taking a spur from it yet again if it passes it IR Zs test then its good to go.
Where these systems can fail is if a plastic CU is fitted and the continuity between earth and the conduit is not there
never seen a house done with screwed conduit ie. couplings & bushes ect. did a lot in 60s with split conduit with rubber gromets on the ends so i doubt if you could rely on conduit for good earth
Clark, there's a lot goes on here which is like site cabin humour. I know you can't tell people's inflection from the written word but the vast majority of it is just good natured ribbing
You'll be surprised to learn that a good many older houses were fully conduited throughout then!! lol!! Even more so, blocks of flats, that when you think about it, makes a lot of sense being as they were primarily concrete floored and ceilings!! Some also being fully wired in MICC cable!!
A lot of the old police houses (when there used to be one every couple of streets apart on estates) were done in conduit
Check by doing an R2 reading, a ELI reading can give a red herring, Ive had decent readings testing Zs on old conduit systems in pre fab buildings, but complete open circuit at the low voltage of an R2 test. damp rusty concrete does conduct at 230V but no so well at 12v
test for zs would have been a good start
If hes unsure of there being an earth in the circuit, i wouldnt be carrying out a Zs test, earth continuity check would be my preference, injecting 25A into a circuit with no earth is dangerous.
No earth on ring main.
Clark3169,
oldtimer,