Recent content by alanmcm

  1. A

    Need help with control panels.

    Theres no maintenance spark on site. I did get help from another guy in work who works with panels. But we couldnt suss out how to get it working as a single cycle button press. More brain power needed, more knowledge needed on my part, hence why im enquiring here as to how others learned and...
  2. A

    Need help with control panels.

    Thanks for the replies, seem to have opened a can of worms. The press worked by pressing the start button and doing one cycle, changing it to a manual way of lowering and raising surely shouldnt make that much of a difference? Theres limit switches on the door, at top and bottom and also a...
  3. A

    Need help with control panels.

    Is there anything out there to help me get my head round control panels and control circuits. I was stuck at a job trying to get a metal barrel press to work automatically. Press start button, press comes down, squashes everything, pressure switch activates and it comes back up and hits the...
  4. A

    3 phase quarry pump

    Went in yesterday morning and disconnected the pump from the circuit and tested the cables again for insulation resistance and all OK. Got the quarry operative to start it up, with the pump disconnected, and it didn't trip. Tested voltages and all were fine. So pump at fault. Didn't get a...
  5. A

    3 phase quarry pump

    There is 2 10mm cables coming down and are paralleled together.
  6. A

    3 phase quarry pump

    Test the windings to earth using an insulation resistance tester. Test between each line to earth and expect quite high readings, over 1M ohm is acceptable but I wouldn't like to walk away from a motor knowing the motor is close to that. Then remove links and go between each line and test for...
  7. A

    3 phase quarry pump

    Didn't take any offence from it, I love learning and find asking a forum of highly qualified and experienced people is better than just trying to muddle through it. Means I can learn different safe techniques and methods to get the result I'm after and to improve the safety. I'm not the most...
  8. A

    3 phase quarry pump

    Good thinking Ill put in place a phase detection relay if there isn't one already, I'm thinking there isn't. Once its lifted out ill test more effectively, my welly boots just aren't made for wading through the water to get to the pump.
  9. A

    3 phase quarry pump

    thanks very much, I will check at the pump itself once its lifted out.
  10. A

    3 phase quarry pump

    the pump is a 3 phase 415v setup. Top shelf - generator and control gear Middle shelf - 32a plug and isolator arrangement, 2 x 32a isolators for each 10mm cable going down and 16a for float. Bottom shelf - pump and pump panel.
  11. A

    3 phase quarry pump

    I tested the cable doing an insulation resistance test. The only way to do that was to disconnect the cables from the pump as they were paralleled and would have led to the same fault on both cables. So when testing each cable for insulation resistance to earth, I found one of the cables was...
  12. A

    3 phase quarry pump

    The cable from the bottom shelf to the pump hasn't been replaced its one of the supply cables that had a fault originally. I'm leaning towards a fault in the pump itself, possibly caused by the pump running on two phases for a period of time. Ill know more in the morning time. Thanks for the...
  13. A

    3 phase quarry pump

    The ends should be linked through the links on the motor terminal block. Control gear all ok, I have disconnected the pump about 15m away from it in the bottom shelf control panel. Theres only 3 wires going over so its linked out delta on the motor terminal block, I can bell between brown and...
  14. A

    3 phase quarry pump

    Latest fact finding mission for you gurus to help me learn about Todays problem was a quarry pump not running, guy went out and meggared the cable and pump and found one of the two 10mm cables was down on the black phase. So while cable was ordered up and being delivered he was called...
  15. A

    Wiring a siren through a timer

    Thanks darkwood.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock