Yes.
I tried to get a reading and re-instate the earth.
It was fluctuating all over the place.
1.4 was my lowest and then is shot back up.
It’s a clearly a break in the earth further down the line.
Thanks for the response.
It’s one supply to the whole building.
If it was 3 different supply’s and two of them had earths, do you really think I would have posted this?
Think about your question.
Equally. Just because it doesn’t have a sweated earth on a 100 year old cable, dosent mean it’s never been earthed or...
I’ll have to peel back the tape to see.
Yes this clamp is DIY.
My point is that it’s always been a TNS system but there’s recently been a break in the earth.
That’s their cable no?
Im currently in a dispute with UK power networks about who is responsible for the incoming earth? Now, i know under normal circumstances the owner has to take responsibility for the external earth, if an earth has never been provided via the normal channels (TNS, TNSC).
This particular...