I see... So you use the measured zs value ( or r1 r2 ) to work out the length of the circuit ( of the line an neutral conductor) and then use the Adiabatic equation to calculate if the short circuit fault condition will comply?
Why do we have maximum Zs values in the regs for RCBO's / RCD's ...
Okay, that makes sense. The Zs of a circuit can give more information about the state and condition of a circuit.
But what I don’t understand is “Why do we have maximum Zs for 61009 RCBO's?”
As an example:
A TT install has a Ze of 55.0 ohm.
The Maximum Zs for a 63A type C RCBO is 0.27 ohm…...