Recent content by Jacko

  1. J

    Contactor wiring help

    Excellent . Thank you Why do they have 8(14) and 7(13)?
  2. J

    Contactor wiring help

    So your saying the switched live in to A1, the neutral in to A2 and the 3 live in at the bottom and out at the top?
  3. 0649B8ED-7F71-43C7-83B7-1F609EF052F1.jpeg

    0649B8ED-7F71-43C7-83B7-1F609EF052F1.jpeg

  4. BF5B2A9D-9A90-49B5-B6EC-7BCCE4DFE108.jpeg

    BF5B2A9D-9A90-49B5-B6EC-7BCCE4DFE108.jpeg

  5. J

    Contactor wiring help

    Hello, I’m need some advice on how a contactor is wired please and where the neutral go. I’m told it is connected to eco 7 and controls 3 heaters in a domestic flat. It stopped working after an electrician did something on a different circuit in the consumer unit. The contactor is an Eaton...
  6. 41D750D1-754D-452E-9BA5-9E1BCB9EA7ED.jpeg

    41D750D1-754D-452E-9BA5-9E1BCB9EA7ED.jpeg

  7. J

    High Zs reading

    Should I be looking for Anything other than a loose connection ?
  8. J

    High Zs reading

    I think I should look again for the loose connection on the CPC, I’m pretty sure the cable is 2.5-1.5. does the result have to be within 1.67 or is it allowed to be slightly over? I was told 1.67 is what we would expect to see so when would you start to look into it?
  9. J

    High Zs reading

    Thank you for your help.
  10. J

    High Zs reading

    Excellent. Would you write that result on the test form and mention the fuse spur somewhere? Thank you
  11. J

    High Zs reading

    I’m not there now but I think it was 2.5/1.5 cable but you have got me thinking now. there was 2 rings in the house, the other readings were L .54 N.53 E.91 that looks like what I would expect for 2.5/1.5 cable. The house was built 14/15 years ago
  12. J

    High Zs reading

    It says on the inside of my EICR certificate book that 1.08 is the max Zs value allowed on a type B 32 amp MCB. Is that correct? if the radial off the ring via the spur is higher than 1.08 but less than the allowed value after a 13amp fuse, which value would you write on the test form? Thanks
  13. J

    High Zs reading

    Hello, looking for some advice on 2 things please. Ive tested a ring main in a house with RCD protection, the results ive had are L-L .43 N-N . 41 E-E 1.17 I had a look for a loose connection but can’t find anything, how high does the CPC reading need to be before you would consider it ‘to...
  14. J

    EICR and outside lighting

    Hello, How would you go about testing outside lights on an EICR if they are supplied off an outside socket? The sockets are supplied off the downstairs ring main, inside there is a 13amp switched fuse spur, then a double pole isolator running outside to 3 x double outdoor sockets all run in...
  15. J

    EICR - can’t find socket

    They had a kitchen fitted so it’s behind a unit somewhere. It will go down as a limitation, thanks for the help

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock