Where fault protection is provided by an RCD, the product of the rated residual operating current (IΔn) in amperes
and the earth fault loop impedance in ohms shall not exceed 50 V.
Hi All,
Thank you for welcoming to this forums
I just want to clarify that the Value I need to enter 100% or 80% in the last column "Maximum Zs Permitted by BS7671"
is it 80% from the table 41.3 from 18th Edition Regs - Page 62 or the value from Pocket Guide 18
Thank you
Loges