Recent content by Mikey10695

  1. M

    Rcd Main switch blown by Ze test

    As soon as I insert a probe on the line, it blows, the tester does Ze, with pfc at the same time.
  2. M

    Rcd Main switch blown by Ze test

    Meter still in working order, I was testing on the incoming line amd main earth, it sparked, bamged and blew the end off the probe as soom as I inserted the probe into the line terminal, the main switch was off, could this be a dodgy main switch rcd as the test function was not initially working
  3. M

    Rcd Main switch blown by Ze test

    Yes the meter was in ze mode, as soon as i put the probe in the line terminal its sparked, banged and blew the probe too
  4. M

    Rcd Main switch blown by Ze test

    I didnt have the neutral probe connected at the time, as I was testing between main income line and the main earth
  5. M

    Rcd Main switch blown by Ze test

    Hi I have a dilog multi meter, it was in ze mode, ive tested other properties all is fine, I switched off the main switch, disconnected the pain earth, as soon as I put a probe in the incoming live terminal the switch sparks and blows, it also took the end off my probe
  6. M

    Rcd Main switch blown by Ze test

    Hi it was an ashley and rock 80amp main switch rcd
  7. M

    Rcd Main switch blown by Ze test

    Hi all just wondering if I could pick you brains, I was doing a ze today on a consumer unit, 80amp rcd main switch, (the test button wasnt functioning so I was already thinking as to what caused this to blow) I disconnected the main earth, turned the main switch into the off position, I then...
  8. M

    Advice on what consumer unit to fit

    I believe 2 of tge 32amps are cooker and hob
  9. M

    Advice on what consumer unit to fit

    Both 40amps are showers, do you think it would be better to get them to bite the bullet and go for a 14 way rcbo board?
  10. M

    Advice on what consumer unit to fit

    Now thats what im talking about ????
  11. M

    Advice on what consumer unit to fit

    Hi ive been recently asked to wire a large property which has been specified to require 13 circuits 2 x 6amps 5 x 32amps 2 x 20amps 2 x 16amps 2 x 40 amps Im just wanting some advice on consumer units, rcd and main fuse sizes A 14 way consumer unit dual rcd would be ideal but im wondering how...
  12. M

    Pvc flex underground

    yes, thats what they have used
  13. M

    Pvc flex underground

    Its a 50mm twin walled duct that complys with EN 61386-24
  14. M

    Pvc flex underground

    Yes the duct is spot on ?? the cable used is fine on taking specific factors in account, personally if the customer agrees I would like to run swa, The rule of thumb ive always used id a cable should be buried a spade and half deep arpund 18inches however because its a fixed surface people are...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock